Posted By: Redsy #6 or #8 NM Cable for Range? - 01/23/04 12:23 PM
On a standard free standing electric range that calls for a 40 amp ckt., I have been using #6 Copper NM Cable.
Does anyone use #8?
Posted By: PCBelarge Re: #6 or #8 NM Cable for Range? - 01/23/04 05:15 PM
If I know that the range is rated at 40 amps, and the run is not too long, I use 8 AWG NM or AC cable. It is rated for 40 amps in the 60 degree celcius column as required in Article 334.

Pierre
Posted By: sparky Re: #6 or #8 NM Cable for Range? - 01/25/04 02:42 PM
As i rarely get any appliance specs beforehand, (other than location) i usually go with #6


~S~
Posted By: ga.sparky56 Re: #6 or #8 NM Cable for Range? - 01/25/04 05:52 PM
I never get any specs either. I'm lucky if I know which side of the kitchen it's on.

I pull #6.

Russell
Posted By: abode electric Re: #6 or #8 NM Cable for Range? - 01/28/04 04:33 PM
Any range that is 12kw or less only needs a branch circuit of 8kw = 33.3 amps at 240v . This can be found in note 4 on the range table 220.19
Posted By: electricman2 Re: #6 or #8 NM Cable for Range? - 01/28/04 06:42 PM