Posted By: Ryan_J Solid or Stranded - 12/27/03 08:56 PM
I have long heard the argument about solid or stranded #8 bonding jumpers being used to satisfy 680.74

I ran into this the other day:
[Linked Image]

[Linked Image]

This is a 1/0 for a hydromassage tub!!! The installer was upset with me for requiring a 1/0 to bond his service lateral conduit, so he decided to bond everything with 1/0.

[This message has been edited by Ryan_J (edited 12-27-2003).]
Posted By: Joe Tedesco Re: Solid or Stranded - 12/28/03 04:19 AM
[quote]requiring a 1/0 to bond his service lateral conduit ..[/quote}

Ryan:

Please explain the scenario?
Posted By: Ryan_J Re: Solid or Stranded - 12/29/03 12:58 AM
Joe: The service entrance conductors are rated for 400 amps. 250.102 (C) refers one to 250.66 for bonding jumpers installed on the line side of the service disonnecting means.

Very popular residentail installation in my neck of the woods.
Posted By: Ryan_J Re: Solid or Stranded - 12/29/03 01:34 AM
THREADJACK!!!

We had a very nice discussion about bonding the line side of a service at this thread:

http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=7;t=000426
Posted By: stamcon Re: Solid or Stranded - 07/30/04 03:08 AM
So, what's the answer to stranded or solid? With the wording "not smaller than a No. 8 solid", is the code describing the actual diameter of the conductor, with a stranded being larger than a solid of the same gage?
Posted By: gfretwell Re: Solid or Stranded - 07/30/04 03:44 AM
I read that as 8 Ga solid or a larger stranded size. The only place I know of that allows stranded 8ga for pool bonding is the bond wire in the PVC raceway to a wet niche forming shell. You can use stranded for equipment grounding (not the same thing).
Posted By: Ryan_J Re: Solid or Stranded - 07/30/04 01:28 PM
As written, I beleive you could use #8 stranded, but I'm not sure that that is the intent.

Compare the language of 680.74 to that of 680.26
Posted By: gfretwell Re: Solid or Stranded - 07/30/04 03:13 PM
I agree 680.26(C) does say "solid copper conductor". I also see that they call the 8ga in the PVC to the forming shell an EGC, not a bond 680.23(B)(2)(b)
I guess there is method to the madness.
Posted By: cpal Re: Solid or Stranded - 07/31/04 03:56 PM
Ryan
What size conductor did the installer wish to bond the service conduit (or conduits??)with??