Posted By: elecbob conduit or NM? - 11/29/03 05:27 AM
A customer has rented space in a single story building with 3 spaces. Each space has 1600 sq. ft. and is seperated by a lathe and plaster wall. His architect says the seperating walls have a 4 hour fire rating and the space can be wired with romex. Any thoughts on this?
thanks
bob
Posted By: nesparky Re: conduit or NM? - 11/29/03 08:48 PM
I would check with the AHJ for the area.
Posted By: Ryan_J Re: conduit or NM? - 11/29/03 11:15 PM
With the exception of an assembly area, you should be fine with type NM cable.

As NEsaprky said, though, check with the AHJ
Posted By: Tom Re: conduit or NM? - 11/30/03 01:24 PM
Also keep in mind that if there will be a dropped ceiling, NM cable would not be allowed above the ceiling as open runs.
Posted By: elecbob Re: conduit or NM? - 12/01/03 03:41 PM
I called the AHJ and romex it is. No dropped ceiling but thank you for the reminder.
bob