Posted By: Ryan_J Service sizing - 11/10/03 09:41 PM
I was asked by a local electrical contractor to stop by their shop and help train the electricians on service/grounding/bonding sizing.

Please take a minute and review this drawing I created. PLEASE let me know if you find any errors in it. Thank you.

[Linked Image]

[This message has been edited by Ryan_J (edited 11-10-2003).]
Posted By: resqcapt19 Re: Service sizing - 11/10/03 10:31 PM
Ryan,
You don't have enough 600 kcmil cables for a 1600 service. You need 4 sets, which changes the line side bonding jumper to 300 kcmil.
Don
Posted By: Ryan_J Re: Service sizing - 11/10/03 10:33 PM
EEK!!!!!

Thats why I posted this! I used the same diagram here that I used for a 1200A!!!

I had this for a 1600A, then I deleted (1) pipe on the feeder and one on the service entrance conductors, but I overlooked changing the rating of the fuses! (embarrassed)

thanks Don!