Posted By: electrician02125 article 210-12B - 09/23/03 12:56 PM
Good Morning -

If I read this article correctly all 125 volt 15 and 20 amp recepticles in dwelling unit bedrooms must be arc fault protected.

Does this include lighting?

Smoke detectors?
Posted By: Ryan_J Re: article 210-12B - 09/23/03 01:09 PM
Yes, it includes both. See the definition of "outlet".
Posted By: PCBelarge Re: article 210-12B - 09/23/03 06:39 PM
The Arcfault breaker issue has many municipalities writing amendments, you should contact your local inspector and ask him, especially when it comes to smoke detectors.

Pierre