Posted By: sparky 250.32 Q's - 06/30/03 10:48 AM
Building A has a service w/GEC's, and a feeder is run from building B to building A (re; subpanel)

~does said subpanel need a GEC if the building already has one?

~if so, should GEC's from different x-formers be married together?

Quote
250.32 Two or More Buildings or Structures Supplied from a Common Service.

(A) Grounding Electrode. Where two or more buildings or structures are supplied from a common ac service by a feeder(s) or branch circuit(s), the grounding electrode(s) required in Part III of this article at each building or structure shall be connected in the manner specified in 250.32(B) or (C). Where there are no existing grounding electrodes, the grounding electrode(s) required in Part III of this article shall be installed.


[This message has been edited by sparky (edited 07-01-2003).]
Posted By: txsparky Re: 250.32 Q's - 07/01/03 01:30 AM
Quote
~ should GEC's from different x-formers be married together?
It is done all of the time. Consider a multi-story building where the building steel is used as the grounding electrode for all of the x-fmers in the building.
Posted By: PCBelarge Re: 250.32 Q's - 07/01/03 09:54 AM
Sparky

Just a 'dumb question', if there is already service in the building why are you running a subpanel to it from another building? Just curious.

Pierre
Posted By: sparky Re: 250.32 Q's - 07/01/03 10:17 AM
Pierre, economics....
the original service (5 meters) is a mess, and at the other end of a long building.

This feeder was available by way of an unsued meter/main nearby
Posted By: resqcapt19 Re: 250.32 Q's - 07/01/03 04:17 PM
sparky,
Are you in compliance with 230.2 and 225.30?
Don
Posted By: sparky Re: 250.32 Q's - 07/01/03 09:18 PM
Don,
it is a feeder, so 230.2 (i believe) would not apply, 225.30 OTOH...
Quote
225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

would seem to consider outbuildings downstream of the main service, limiting the # of feeders or branch circuits per stipulations.

there are two building on the same property here, via the same owner, each has a service drop.

Building A is a large long 5 unit apt house w/barn.

Said barn is being supplied from building B's exclusive service, via a feeder to A


what am i missing?

~S
Posted By: resqcapt19 Re: 250.32 Q's - 07/02/03 02:33 AM
In my opinion, you can't feed a building that already has a service with a feeder from a second building. You need to check with the AHJ before making this installation. The code intent is to have a single source of supply for each building.
Don
Posted By: sparky Re: 250.32 Q's - 07/02/03 10:33 AM
hmmm, well if it is pertinent,i believe the barn that is fed here has been ordered firewalled off from the rest of the building.
Posted By: Gwz Re: 250.32 Q's - 07/02/03 11:41 AM
I agree with Don about a building having only one supply source.

BUT, what would happen if a 1 to 1 isolation transformer was installed in the feeder of a second source to a building. Would this be considered separately derived?


Article

100 Service
100 Feeder
100 Separately Derived System
100 Premise Wiring (System)
230 cover utility supplied
250 covers GROUNDING.

and probably other Articles.
Posted By: tdhorne Re: 250.32 Q's - 07/17/03 11:07 PM
Take pitty on us poor jakes (firefighters) and at least clearly mark both disconnecting means to indicate the two supplies and their locations.
--
Tom
Posted By: sparky Re: 250.32 Q's - 07/17/03 11:50 PM
Respect, not pity Tom, i've marked it well, even the LB that comes into the building states the source

(visible from said LB)

of course, you'll not find that in the NEC either

opinon is such an objective/subjective animal eh?