Posted By: Reel-Break Paint shop - 05/05/03 12:27 PM
I have a question We`re putting in some crouse-hines Illuminator fluoresant lighting in a paint shop new area they are sealed and approved for the area.My question is we have a seal where conduit enters new room and the fixture is sealed If there are no connections in the condulets between two seals can they be standard condulets (t`s and lb`s) or would they also have to be rated for the location. Thanks in advance
Posted By: resqcapt19 Re: Paint shop - 05/05/03 01:11 PM
Is the area Div 1 or Div 2? If Div 1, then 501.4(A)(3) requires explosionproof fittings.
Don