Posted By: Edward 2 prong receptacle to 3 prong redeptacle/GFCI - 04/11/03 09:55 PM
I donot have a 1990 code book can somebody check to see if GFCI was a requiremnt for replacing two prong outlet.(without EGC)

Thank you
Edward
Yes, as per 210-7 (d) exception in the 1990 NEC book on page 70-35.
Edward,

1990 NEC 210-7(d)Ex. allows a GFCI Receptacle to replace a 2 prong receptacle where a grounding means does not exist.

Bill
Harold,

I guess you type faster than I do!

[Linked Image]
Bill
Guys,

Don't have a 90 NEC, but I believe it does not "require" a GFCI but "allows" it.

Bob
Bob,

I did say "allows", but if a 3 prong receptacle is to be installed where there is no grounding means, GFCI protection is required.

[Linked Image]
Bill

[This message has been edited by Bill Addiss (edited 04-12-2003).]
Bill,
You said "allow", Edward said "requirement", but you are right on the GFCI if you go to 3 prong and don't provide a ground.

How do you get that smiley in the text body?

Bob
Bob,

Look here for your smilies: https://www.electrical-contractor.net/ubb/faq.html#smilies

Curt