Posted By: Bobby Mercier TABLE 430.52 - 12/13/02 08:34 PM
Does PERCENTAGE OF FULL LOAD CURRENT mean
the full load current on the motor nameplate or in table 430.150

Bobby Mercier
Posted By: walrus Re: TABLE 430.52 - 12/13/02 09:03 PM
I believe its on the nameplate but some motors don't list it hence the table
Posted By: resqcapt19 Re: TABLE 430.52 - 12/13/02 09:17 PM
See 430.6(A)(1).
Don

[This message has been edited by resqcapt19 (edited 12-13-2002).]
Posted By: Bobby Mercier Re: TABLE 430.52 - 12/13/02 09:27 PM
Walrus it's
for sising the motor branch-circuit short-circuit protective device. see table 430.52.....

[This message has been edited by Bobby Mercier (edited 12-13-2002).]
Posted By: Bobby Mercier Re: TABLE 430.52 - 12/13/02 09:30 PM
Thanks