I posted a message a few weeks back and received some tips. Since then I also have found a source to tell me what states are implementing the AFCI breaker. But some states are enforcing the article based on the 1999 NEC and others have adopted the 2002 NEC. I really don't have a source for the NEC book to read the ruling so that is why I need someone's help here. This request is coming from Canada. Thanks to all, in advance, who respond.
Posted By: Ron Re: Article 210.12 - 06/05/02 01:04 AM
The differance between the 1999 and 2002 is that the 1999 requires bedroom receptacle and the 2002 requires all bedroom outlets (lights, smokes, recepts, etc.)
Posted By: sparky66wv Re: Article 210.12 - 06/05/02 04:38 AM
Ken, may I add that the requirement is for 120V circuits, 240V is not required to have AFCI protection, and multiwires are apparently out of the question. (Cutler Hammer makes the only 2 Pole AFCI Breaker that I'm aware of...)