hi,
i cant find any restriction on running ac/bx through the floor on a residential job...
anybody know of any restrictions?
thanks
frodo
Do you mean within a wall or exposed?
--
Tom
hi,
the ac/bx is run through the floor to a handy box mounted on the baseboard.
-regards
frodo
320.10 Uses Permitted.
Where not subject to "physical damage", Type AC cable shall be permitted as follows:
(1) In both exposed and concealed work .....
The key is "physical damage" ---- and at the floor level, there can be a possibility of damage caused by a floor polisher or other equipment. I would use a piece of rigid metal conduit as a sleeve just to be on the safe side.
thanks
[This message has been edited by frodo (edited 05-13-2002).]