Posted By: frodo AC/BX Cable run through floor - 05/06/02 03:24 AM
hi,
i cant find any restriction on running ac/bx through the floor on a residential job...

anybody know of any restrictions?

thanks

frodo
Posted By: tdhorne Re: AC/BX Cable run through floor - 05/13/02 06:15 PM
Do you mean within a wall or exposed?
--
Tom
Posted By: frodo Re: AC/BX Cable run through floor - 05/13/02 07:07 PM
hi,
the ac/bx is run through the floor to a handy box mounted on the baseboard.

-regards

frodo
Posted By: Joe Tedesco Re: AC/BX Cable run through floor - 05/13/02 08:59 PM
320.10 Uses Permitted.

Where not subject to "physical damage", Type AC cable shall be permitted as follows:

(1) In both exposed and concealed work .....

The key is "physical damage" ---- and at the floor level, there can be a possibility of damage caused by a floor polisher or other equipment. I would use a piece of rigid metal conduit as a sleeve just to be on the safe side.
Posted By: frodo Re: AC/BX Cable run through floor - 05/14/02 12:57 AM
thanks