frodo;
the barns i've done have only the 'luminare' in the actual stall. Everything else i try and talk into the adjacent feed,tack room.
This , not only for code related & economic reasons, but also considering a 1200lb orney animal
( i gotta lotta holes kicked in my barn )So the following would be my focus....( 2002)
547.8 Luminaires (Lighting Fixtures).
Luminaires (lighting fixtures) shall comply with the following.
(A) Minimize the Entrance of Dust. Luminaires (lighting fixtures) shall be installed to minimize the entrance of dust, foreign matter, moisture, and corrosive material.
(B) Exposed to Physical Damage. Any luminaire (lighting fixture) that may be exposed to physical damage shall be protected by a suitable guard.
(C) Exposed to Water. A luminaire (fixture) that may be exposed to water from condensation, building cleansing water, or solution shall be watertight.
Also note the latest wiring methods...
547.5 Wiring Methods.
(A) Wiring Systems. Types UF, NMC, copper SE cables, jacketed Type MC cable, rigid nonmetallic conduit, liquidtight flexible nonmetallic conduit, or other cables or raceways suitable for the location, with approved termination fittings, shall be the wiring methods employed. Article 398 and Article 502 wiring methods shall be permitted for areas described in 547.1(A).
FPN:See 300.7 and 352.44 for installation of raceway systems exposed to widely different temperatures.
(B) Mounting. All cables shall be secured within 200 mm (8 in.) of each cabinet, box, or fitting. The 6-mm (1/4-in.) airspace required for nonmetallic boxes, fittings, conduit, and cables in 300.6(C) shall not be required in buildings covered by this article.
Note the interesting commentary....
Cables must be secured within 8 in. of cabinets, boxes, or fittings installed in agricultural buildings. This distance is less than that required for cables in other types of occupancies. The requirement for a 1/4-in. airspace in 300.6(C) is judged unnecessary in agricultural buildings, provided nonmetallic wiring methods are used. Decreasing the support spacing requirements coupled with eliminating the 1/4-in. airspace requirement reduces the potential for mechanical damage to cable-type wiring methods. Locating the wiring methods directly on the interior surface of the building allows a sealant to be placed along the wiring method to facilitate cleaning. See also 300.6(C), Exception.
Joe,
Does NFPA 150 say, or elude, to boardering a horse(s) ?, as this is common practice...