ECN Forum
Posted By: aldav53 sharing circuits - 12/07/01 02:25 AM
Is it legal to install a individual circuit such as a 240v 30a and put in 2 receptacles instead of one, if the loads would not be used at the same time?
Posted By: Nick Re: sharing circuits - 12/07/01 02:41 AM
What you want to do looks code compliant per 210-21 and 210-23.
Posted By: Steve Miller Re: sharing circuits - 12/07/01 10:47 PM
I know of nothing that says a 240v 30a ckt can only have one outlet. In a residence we normally only put one but that's because we need only one.
© ECN Electrical Forums