I was looking at a prospective job yesterday and was told by the owner that he was told he had to replace everything with a 400a service. Conductor sizes were fine. The arrangement was an overhead fed meter, to a gutter below, a 100a breaker panel on the right, a 100a disconnect on the left to a subpanel, and a 200a disconnect on the left to a subpanel. The owner thinks the issue had to do with this being 3 phase and feeding the 200a panel. Is there enough information here to guess what might be wrong that would require replacing this with a 400a service, CT can... the whole enchilada?
Posted By: Scott35 Re: 3ph 200a + 100a + 100a - 10/06/01 08:35 PM
If the subfeeds / subpanels will have increased loads connected to them [like 50% or more of their maximum capacity], plus the loads will be running at the same time ,along with 3 hours or more [LCL], than this new load calculation might very easilly exceed the existing service capacity.

Is the existing service 200 amps?

If this Client plans to draw high loads and expand in the future, the 400 amp service is a valid concern.
Calc the project out, then figure out what is the best way to go.

Scott SET
Posted By: Redsy Re: 3ph 200a + 100a + 100a - 10/08/01 01:54 AM
No, there is not enough information.
Please clarify...
WHO told the owner to replace everything?
What do you mean "the conductor sizes look fine"?
Being 3 phase has no significance.
What is the existing load demand?

[This message has been edited by Redsy (edited 10-07-2001).]
Posted By: WARREN1 Re: 3ph 200a + 100a + 100a - 10/08/01 03:50 PM
Not enough information. And yes, 3 phase will make a difference for phase load balance, which will be of some concern. We try to keep phases balanced within 10% on the connected load schedules.
Posted By: Redsy Re: 3ph 200a + 100a + 100a - 10/09/01 12:56 AM
Warren,
I still don't understand why it being a 3 phase service has any bearing on whether an upgrade is needed. I think the main concern is load calculations. The panel layout may be a matter of convenience.