Posted By: Joe Tedesco Article 645 - 07/19/01 02:43 PM
Why is it OK to have liquidtight flex and nonmetallic conduit (both having a PVC jacket ) under the raised floor, but not PVC with
a ground conductor in it?

Joe Lusso, Electrical Plant Engineer
Facilities Project Management
303.673.5248 phone
303.673.4551 fax
email: LussoJA@louisville.stortek.com
Posted By: Redsy Re: Article 645 - 07/19/01 03:58 PM
Doesn't 645-5 (d) (2) permit rigid non-metallic (PVC) conduit?
Posted By: Joe Tedesco Re: Article 645 - 07/19/01 05:13 PM
Redsy:

Yes, and the question is really not very clear. I have invited the person who asked this question to come aboard here on theis BB and look for the help he needs. I always bring these types of question here so we can all put our thoughts into the discussion.
Posted By: tdhorne Re: Article 645 - 08/05/01 04:33 PM
Quote
Originally posted by Joe Tedesco:
Why is it OK to have liquidtight flex and nonmetallic conduit (both having a PVC jacket ) under the raised floor, but not PVC with
a ground conductor in it?

Most of the limitations on the use of PVC conduit inside buildings are the result of concerns about the fuel and smoke contributed under fire conditions rather than its performance as a raceway.
--
Tom