Posted By: tsolanto A/C Disconnect height - 07/22/15 01:39 PM
I was wondering your thoughts on this issue. Recently I have noticed that HVAC contractors have been mounting mini split compressor units 12 feet off the ground attached to the house. The disconnect is mounted right next to the unit at the same height. So, I am wondering what you guys think about 440.14 and do you think this meets the requirement of being readily accessible to the unit.

Posted By: HotLine1 Re: A/C Disconnect height - 07/22/15 02:17 PM
Are these locations subject to flood elevations??

ie: BFE which is base flood elevation, which dictates the lowest height for electrical (and mechanical) equipment.

Local municipal ordinances also may require 'BFE+x feet"

BFE is based on FEMA flood maps. This is all aftermath of the major area flooding from hurricane Sandy in this area, and other storms in other areas

Posted By: tsolanto Re: A/C Disconnect height - 07/22/15 02:32 PM
No it is not.
Posted By: gfretwell Re: A/C Disconnect height - 07/22/15 05:09 PM
How do they service the unit? The disconnect should be accessible to the tech while he is working on the unit.
Posted By: tsolanto Re: A/C Disconnect height - 07/22/15 05:47 PM
I agree but 440.14 says it needs to be readily accessible from the unit. Readily accessible does not allow climbing on portable ladders. Also what if the tech is on the ladder working on the opposite side of the unit that the disconnect is on? Even if you use the argument that the disco is readily accessible from the unit if the ladder is placed by it you can't make the argument that it is with the ladder in the other side.
Posted By: renosteinke Re: A/C Disconnect height - 07/23/15 12:15 AM
Thanks for the elaboration; I was thinking BFE was a reference to the rural areas near Cairo, Illinois laugh

I see no problem with mounting a disconnect adjacent to the equipment it serves. It needs to be accessible while the unit is being worked on.

I'll bet this mounting is an attempt to make the unit less vulnerable to thieves. They may have also been trying to reduce line length, which has a major effect on the efficiency (SEER) rating of the system.

I'd also be more concerned with whatever is UNDER the unit. "Accessible" becomes moot if the area itself is blocked. (There's a reason I keep pruning shears on the truck).
Posted By: HotLine1 Re: A/C Disconnect height - 07/23/15 02:13 AM
OK, let's see if I can clear this up....

Working access would be from a ladder in some cases; the platform must provide working space on three sides of the CU.

Note that this is mandatory in flood plain areas as designated by FEMA's latest flood maps. FEMA regs are mandated by the local flood plain manager. FEMA regs are made mandatory by the NJ DCA, the State authority.

Based on that, there are CUs that are 12' above dirt, with a disco next to the unit.

The above applies to NJ areas that are in flood zones, and is the result of the extensive flood damage from Sandy, which also affected parts of NY metro area,

While I was the AHJ in a town that was decimated by Sandy, the BFE heights/zones were in a state of flux from FEMA. Replace a flood damaged service, the meter must be a BFE+2' (Twp Ord was the "+2') which put the POCO meter in some cases 10-12' above dirt. The POCO bitched, FEMA won. After many months of this, the POCO, FEMA, and DCA agreed that the meter must be at 5' above grade, BUT everything else must be at BFE+2'. This means, no meter/mains; no meter stacks. An 'around this, with local zoning, planning approvals would be to install a 'deck' or porch with a staircase and install the meter/main, meter stack there with compliant working clearances.

BTW, 'house raising' seems to be a tremendous grouth business here along the Jersey coast!!

Did I like enforcing the above, NO; but I had to. Many services were done twice; a few more than twice.

Again, I will say...this is mandatory in any area designated by FEMA as a flood zone. I do not know if tsolanto's area of Long Island, NY is a FEMA zone.
Posted By: HotLine1 Re: A/C Disconnect height - 07/23/15 02:19 AM
BTW, after Sandy, there was a lot of FEMA books, CDs/DVDs regarding flood areas, flood zones, heights, construction methods, etc. Problem was, finding time to read/view it.

Sandy decimated a large swath of Jersey/NY areas, and to this day, there is a LOT that require attention, help, reconstruction, etc.
Posted By: tsolanto Re: A/C Disconnect height - 07/24/15 01:23 AM
Hotline, thanks for the input. What I am seeing is definitely not is a flood zone... I am an electrical inspector for NYC and the work in question is being done all over Queens and Brooklyn. The thing that concerns me is that the definition of readily accessible does not allow portable ladders, but 440.14 seems to require the disconnect readily accessible from the unit. So it requires the disconnect up by it but IMO I can't see how it is readily accessible if you climb a ladder to get to it. 404.8 gives allowance for a disconnect to be mounted above 6 foot 7 inches but 404.8 is not referenced in 440.14 or anywhere else in 440 so IMO you can't use it. I wonder if this is something relatively new and should be cleared up in future editions of the NEC.
Posted By: gfretwell Re: A/C Disconnect height - 07/24/15 03:23 AM
I have seen a lot of discussion about this with piling houses at the beach but I am not sure if I ever heard a good answer. A few suggestions were decks around the unit, accessible from the dwelling or some kind of permanent stairs/ladders. We get the same kind of questions about air handlers swinging from strut in the ceiling of garages. The question about working space also comes up with air handlers in closets.

The best I can tell, inspectors just hold their nose and approve most of these things if another answer is not forthcoming.

Years ago they let them put the condensers at grade, even on a piling house but FEMA and the insurance companies stopped it. They even have to put water heaters at FF level in garages. That means they are building a raised platform and again the disco may not be <6'6. If it is near the steps, you can make it work.
Posted By: tsolanto Re: A/C Disconnect height - 07/24/15 01:13 PM
Thanks Greg I guess I will put my blinders on on this one. Appreciate the feedback!
Posted By: gfretwell Re: A/C Disconnect height - 07/24/15 06:40 PM
You should get together with the other AHJs around you and come up with uniform policies so you are not making the contractors nuts. Nothing worse than having different interpretation of rules in every place you work. (OK here but a tag across the street) Occasionally that is not possible but it is a goal.
Posted By: tsolanto Re: A/C Disconnect height - 07/24/15 07:13 PM
That actually is my intention. So difficult to do though. Thanks again.
Posted By: HotLine1 Re: A/C Disconnect height - 07/25/15 06:07 PM
Greg:
Just an FYI; the subject of requiring 'stairs' to access the POCO meter when it was BFE+2' was 'no, stairs cannot be required by the inspectors'.

It was a lot of mass confusions until the POCO and FEMA/DCA all agreed on the meter only at 5' above grade.

I'm happy that I do not have to deal with this anymore.

Posted By: HotLine1 Re: A/C Disconnect height - 07/25/15 06:09 PM
tsolanto:

Does the area you are referencing have any local ordinances regarding the heights??

The Boro I worked in was BFE plus 2', with the +2' being a Boro ordinance.

I had to read and grasp the FEMA flood regs, flood maps with zones, revised regs, revised flood maps, revised FEMA/DCA and JCP&L regs.



Posted By: tsolanto Re: A/C Disconnect height - 07/26/15 12:33 AM
In some areas, probably flood zone I believe there is a height requirement. There is a program called ""Build it Back" that the City organized a year or so ago. Those inspectors inspect the Sandy damaged areas. So I don't know the exact requirements since I don't inspect them. If you needed some info I would be happy to find out for you John...
Posted By: HotLine1 Re: A/C Disconnect height - 07/26/15 01:12 AM
tsolanto:

Thanks for the offer of info, but I have enough, in print, CD/DVD formats.

The DCA provided lots of info for Building, Electrical, Plumbing and Fire Subcodes & Inspectors regarding flood zones, etc.

You may have some installs that are on or near a flood map zone border who elect to comply with the flood zone requirements on a voluntary basis.

As I said above, I have no regrets for leaving the town in the flood zone.