Posted By: Yoopersup Markings required on Disconnects, OCD,ect - 08/27/14 08:00 PM
I'm looking for Code references on Marking requirements
on Disconnects, Switchboards ,Overcurrent protection ect
by the NEC. such as 110.22 / 408.4.
I thought there was more detail on circuit markings??
70-E brings up all sources of power must be disconnected (electrically safe condition).
But as far as I see nothing requires the sources be labeled
at the equipment??
Yoopersup
Yoop:

IMHO, the circuit ID at receptacles, etc. is a design/spec item. I can't cite anything within the NEC.

The spec for the hospital in my town requires circuit/panel ID on all receptacles, switches, data/comm jacks, etc. The data center also has the same spec, as do some other commercial locations.

I see where you are coming from with this, but...it may fall back into the 'qualified person' heading.

As to disconnects, controllers, etc., again, without an NEC article, that also falls to 'spec' or good trade practices.