Posted By: watersparkfalls 400 amp remote service - 10/28/13 12:34 AM
I am going to bring 400 amp service to a remote location, meter only no disco's till they terminate at their locations one to the house the second to the shop; The house has a ufer to establish service, however the shop doesn't have a ufer. Would I be required to establish its service at the remote location and bring 4 wires to the shop or can I still establish service at the shop and use 2 ground rods in lieu of ufer? Thanks sparky
Posted By: gfretwell Re: 400 amp remote service - 10/28/13 01:21 AM
Two separate buildings can have 2 services off the same drop or "may poled" from a single metered pole in the middle.
I would ask the AHJ how they feel about sending service conductors, building to building after the meter but I can't imagine how it isn't legal.
Posted By: HotLine1 Re: 400 amp remote service - 10/29/13 07:43 PM
If there is no Ufer available, and no footings being installed, then you must use any other available grounding electrode.

With nothing else (Ufer,water,steel,etc) you must install rods, ring, plate.