Does anyone have a copy of the 1993 NEC to see what it stated as to how far away overhead service wires must be from the parimiter of a pool.
It would be greatly appreciated
Thank you
The picture is the same as 680.8 but the clearances are shorter
_______________________________________________________________________
A. Clearance in any
direction to the
water level, edge
of water surface,
base of diving
platform, or
permanently-anchored raft
Insulated Cables, 0–750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor
18 ft
All other conductors
0-15kv
25 ft
>15kv
27 ft
_______________________________________________________________________
B. Clearance in any
direction to the
diving platform or tower
Insulated Cables, 0–750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor
14 ft
All other conductors
0-15kv
16 ft
>15kv
18 ft
_______________________________________________________________________
C. Horizontal limit
of clearance
measured from This limit shall extend to the outer edge
inside wall of the of the structures listed in (1) and (2)
pool above but not less than 10 ft.
_______________________________________________________________________