Posted By: sparkync Size feeder?? - 12/23/12 01:37 AM
I have an industrial customer who is wanting a 200 amp feeder to feed a 120/208 3 phase panel. They sent me the specs for the machines that are going to be used in the panel. He list (3) douple pole 20 amp 240 volt circuits,(5) 30 amp 240 volt circuits, (4) 20 amp. 120 volts, (1) 15 amp 120 volt circuit, and (1) 5 amp 120 volt circuit. At this point I can only assume that this is the running current. The total amperage of these machines is 310 amps. If I read the code right for these machines there are no reductions for this kind of feeder that can be applied, and a 200 amp feeder will be too small. The feeder is to come off of a 120/208 buss duct and feed the panel. Any input on this? Am I reading the code right here? I guess I need to see if the information he sent me is the actual running current or just the overload protection device. Any input would be appreciated. Also I have plans of using a fusible plug in unit on the buss duct and feeding to a main lug panel. The plug in disconnect will be around 20 to 25 ft. in the air. Is this still permissable to use the main like this even if it is not readily accessible? Thanks again.. Steve
Also I guess I need to ask him if all these machines will be or will be capable of running at the same time...
Posted By: Tesla Re: Size feeder?? - 12/23/12 03:49 AM
To simplify the math for the 3-phase calculations...

The first three 30A 2-pole breakers are identical in load to two 3-pole breakers if they are mounted down the left side:

[ A&B, C&A, B&C = A&B&C + A&B&C => ckts 1,3,5,7,9,11 used.]

The next two 30A 2-pole breakers PLUS the first two 20A 1-pole breakers are LESS demanding than two more 3-pole breakers at 30A:

[ A&B, C&A,B,C < A&B&C + A&B&C => ckts 13,15,17,19,21,23 ]

Lastly, the last two 20A 1-pole PLUS 1 15A 1-pole is LESS demanding than one more 3-pole breaker at 20A:

[ A,B,C < A&B&C => ckts 25,27,29 ]

The last, odd 5A 1-pole circuit can be dismissed as irrelevant; it's too small to affect the calculation as we can see:

We have nearly balanced our phases with four (2+2) 30A 3-pole equivalent circuits and one (1) 20A 3-pole circuits.

Each feeder phase will see only its draw which is 4 x 30A PLUS 1 x 20A --- 140A per leg of Y connected power.

Since you've got 3/0 if not 4/0 conductors you're way, way into the clear. 125% of 140A is 175A.

The 5A 1-pole circuit is just frosting on the calculation. It doesn't matter which phase it hits.

=======

As regards Bus Duct taps...

They have their own tap exceptions in the NEC...

And in an industrial setting this arrangement is the norm -- nothing special at all.

http://www.salingerelectric.com/

Talk to these fellows. They work that end of the street all the time. They deal in scrapped out Detroit assembly lines.

If your patron can accept second-hand industrial rated gear, some bucks can be saved.

(I have no connection to Salinger Electric. Web search is your friend.)
Posted By: Tesla Re: Size feeder?? - 12/24/12 12:56 AM
One last point:

Breakers used to feed motors are sized to withstand the inrush current that they draw.

This means that, unlike resistive loads, the running current from a breaker to a motor load will typically be about half of the nominal breaker rating.

e.g. a 35A 2-pole breaker will be mated to a motor that draws 17 A in normal, full-load service.

So, the customer's feeder conductors are even more conservatively sized than the above, quick-snap calculation implies.

=========

His actual running loads are not even tapping half the available feeder current -- almost certainly.
Posted By: Trumpy Re: Size feeder?? - 12/24/12 03:23 PM
Tesla,
Circuit protection is designed to protect the down-stream cables, not what is on the end of them, this is electrician 101.
Posted By: Tesla Re: Size feeder?? - 12/24/12 11:28 PM
I'm not going to dive into the upside down peculiarities found in 430.

I'll just reference the fact that -- in the extreme -- for motor circuits only -- the NEC actually permits a 50A breaker to service a #12 conductor pair.

Uniquely, the high inrush currents of inductive motors don't mate up well with the common NEMA circuit breakers that we all know and love.

So, the Code permits a separate set of calculations -- and ( belt & suspenders ) insists upon what amounts to a 'mated' OCPD -- permitted to be even integral to the design of fractional horsepower motors. (With NEMA dictating their design, too.) When the motor is larger, the NEC specifies that this second current protection be provided via one scheme or another. The most popular, by far, is by time-delay fuses set in a disconnecting means close by the utilization motor.

The conductors will be actually protected by the time-delay fuse -- and the breaker reduced to being a switch -- with the breaker providing a casualty-trip back-up 'trip' in case of collision or earthquake.

For motor circuits, the conductors are sized for normal running at full load PLUS an 'insurance' margin of 25%. NEMA fuses, for motor circuits, are designed to tolerate the in rush and yet blow before the conductors are stressed -- a value that will always be lower than the start-up surge that the conventional NEMA circuit breaker must let pass.

===============

It was decided ages and ages ago, that it would be most unwise to have two circuit breaker time-current performance curves circulating all over America. For, it was a certainty that someone would substitute the wrong C/B -- leading directly to either fire -- or a penny patch-around.

So, NEMA decided that -- for ordinary 1 and 2-pole circuit breaker only one time-current characteristic ( actually a band of acceptable performance ) would be: that of lighting and appliance loads.

Further, that all small motors would be protected by other NEMA standards so that mass produced consumer retail devices were impossible to screw up even if installed by a hack or homeowner.

And finally, that 3- phase devices, stuff always installed by professionals (almost), would be protected by provisions in the NEC, and not integrally within the machines.

==========

If you're not wiring up multi-horsepower motors in a NEMA environment, then the above does not apply.

Overseas, especially France, fuses mated to the load are the norm. In such a scheme, none of the above logic/ design trade-offs apply.

In a fuses only scheme, you install the correct fuse for the load type -- and are done with it.

Exotic 3-pole C/Bs do exist that have motor-startup time-current performance mated to loads. NEMA does make them. These days, they can even be adjusted in the field. But they're not priced like Chicklets -- and are spec'd by EEs. ( With a big assist from the factory tech rep.)

Having said that: it's as common as dust for up-sized conductors to run to all moderate motor and HVAC loads. It's often called out in the contract specs... or dogged conservatism rules the day.

No-one ever gets red-tagged because they wasted copper on over sized conductors. Such a thing only hurts the person paying for it.

=========

I once ran a cost-plus job, a retro-fit. My employer ran grossly oversized HVAC feeders at every turn. He just &^%$ the owner-developer -- who was squeeling every step of the way. He hired on an independent expert only too late.

The HVAC system used (25 x 2) 50 hp at 200V 3-ph.

He ran twin 2.5" EMT stuffed with 400kCMIL 3-ph, each and mounted a 400A NEMA3R diconnect. (Installing it was brutal, it was on the roof of an unfinished retrofit. No elevators, missing stairs, etc.)

Though wildly overbuilt, it sure passed inspection; and without a murmur.

(Came in after it had been 40% installed. I was shocked as to its oversizing.

The prior foreman had been red tagged for installing EMT below grade, in concrete. That use was specifically prohibited by local (city) code.

I did get all of my work inspected by the city's top inspector. No-one else was permitted to inspect downtown office high-rises, by order of himself.)

Posted By: Scott35 Re: Size feeder?? - 12/27/12 09:36 AM
Nice Motor Circuitry descriptions post, Tesla!

I have dealt with many complaining Persons, over the Years, when applying Article 430 allowances to Motor Circuits - be it in the Field, or per my Plan Sets.

Most Commonly heard statements:
"You Cannot use #6 THHN CU. with a 90 Amp Breaker"
or
"You Cannot use #4 THHN CU. with a 125 Amp Breaker"

I guess the responses:
"Right; I could have used a 125 Amp Breaker with the #6s"
and/or
"Right; I could have used a 175 Amp Breaker with the #4s"
was more smart-aXX than resourceful! wink

--Scott (EE)
Posted By: sparkync Re: Size feeder?? - 12/27/12 06:50 PM
On this 120/208 3 phase feeder, is there any deductions I can allow on the neutral? The Code calls for 3/0 for 200amps. for copper conductors. If I am reading right, according to 220.61 (C) in the 2005 Code( don't have my 2011 code handy) says there is no reduction allowed on a 4 wire 3 phase wye connected system. Just wanted to verify. Thanks...
Posted By: sparkync Re: Size feeder?? - 12/28/12 12:58 AM
"I'm planning on running 2" EMT with (4) 3/0 copper thhn conductors with a # 6 thhn ground. The length will be approximately 25ft. in the air, coming out of the buss duct switch. I'm planning on securing the emt with beam clamps (CADDY BC200-CD5B). The specs on the caddy clamps say the static load limit is
100 lbs. I assume that this means that the weight at the clamp cannot be over 100 lbs., therefore if I install sufficent amount of clamps, I should not have a problem with it falling or moving, right? thanks for the input..
Steve..
Posted By: Tesla Re: Size feeder?? - 12/28/12 02:23 AM
Strictly speaking, you've got zero three-phase loads.

You can't count on load balance -- one must design for the absolute worst load imbalances possible. At some point in the future they'll happen.

So, there's no way you can justify reducing the neutral in this situation.

===========

In these situations it's extremely common to run MC in cable trays -- or to use industrial rated cable drops -- from Bus Duct Plugs.

I'd get on the phone to Salinger without delay.

=========

In a typical factory, Bus Duct is run along either a wall or high, straight across the factory floor. ( Open space, flexible assembly )

From there power is tapped by Bus Duct Plugs (They're massive - no corelation to NEMA cord caps at all.) with cable drops down to manufacturing cells/ distribution panels at floor level. These drops always have some strain relief device and protection from mechanical casualty. ( Bollards and cages, e.g. )

Not uncommonly, there is a provision for a top-side disconnecting switch at the Bus Duct Tap which is operated by a pull cord/ rope. See the NEC Handbook for illustration.

The drops are massive cable assemblies that can stay in service for ever and ever.

The other 'new-wave' approach has been cable tray and industrially sized MC. (Even 750 kCMIL is available.)

There has been a long term shift towards aluminum and away from copper. It's the $$$$$.

===========

Unless you're a blood relative to the client, I'd avoid getting so far afield from your prior experience.

One last thing: don't make any attempt to tap the Bus Duct while it's energized.

Bus Duct is a whole sub-specialty -- with all manner of gotcha details and materials -- that is sure to embarrass a noob.

You need to sub-contract with / hire on a j-man who's done the deed before.

As for 100# static loads -- I can't fathom your geometry/ installation set-up.

If the panel is to be set 25 feet below the Bus Duct -- why would you use anything but cable?
Posted By: gfretwell Re: Size feeder?? - 12/28/12 02:35 AM
Yup that is the weight on each clamp. I think you are well within that using a 10' or less between supports.
Posted By: sparkync Re: Size feeder?? - 12/28/12 07:17 PM
Thanks Greg and Tesla. That's what I figured it had to be on the clamps. I always like to cover all my bases when going into a job. Most of the time I overdo it, but I'd rather over do than under do. As far as doing something out of my field, Electricity is my field. I do understand there is a lot I have not done, and I'm very careful to try and not get in over my head. Work is scarce and I cannot afford to turn down work if there is a possibility I can do it.
To Tesla: As far as cable is concerned for a drop, I HAVE NOT seen a 3 phase 200 amp copper feeder cable with a ground and neutral. Do they make such a thing? If so, looks like it would be so heavy it would not be feasible to hang from the ceiling. Be like fighting a giant Anaconda snake smile
Thanks for all the input.. Steve
Posted By: gfretwell Re: Size feeder?? - 12/28/12 07:40 PM
Southwire Armorlite MC cable comes in 3/0-4 with ground (black/red/blue/white and a bare ground)
I bet it ain't cheap and I am sure it will be a special order in most places but it is available.

http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet262

It says it weighs 2.8 pounds a foot. (2709 per m)
Posted By: sparkync Re: Size feeder?? - 12/29/12 08:22 PM
Wow!! This age of technology never ceases to amaze me. I learned a long time ago that I don't know everything:)
Posted By: sparkync Re: Size feeder?? - 12/29/12 08:44 PM
Greg, what page of Southwire did you get this information. I would like to know the cost of (4) 3/0's with a ground in this cable. Be interesting to compare the cost with installation in pipe.. Thanks, Steve
Posted By: gfretwell Re: Size feeder?? - 12/29/12 09:28 PM
http://www.southwire.com/products/ArmorliteTypeMC.htm

This is on their web site.

I am not sure about prices and minimum orders. I would start with my local dealer.
Posted By: HotLine1 Re: Size feeder?? - 12/30/12 12:54 AM
One drawback I heard from an EC was the support requirements for the MC feeder size was not thought about when he switched from pipe to MC feeder. He was not a happy guy!
Posted By: Tesla Re: Size feeder?? - 12/30/12 02:17 AM
I don't work the industrial side of the street, but my general impression from NECA shows is that cable tray holding MC up through feeder sizes has taken off.

Greenlee has a whole series of specialty tools entirely directed at pulling in MC -- over pre-existing MC -- in industrially sited cable trays.

For the situation at hand, you might be well off buying even second hand MC from Salinger or its competition. You only need a trivial amount.

BTW, the big move has been to aluminum -- to include Bus Duct.

IIRC Westinghouse invented Bus Duct and put it on the market circa 1938. Eventually that division made its way to Cutler Hammer.

As popular as it is for industry, Bus Duct took off in the high rise sector. Tugging in big conductors vertically is brutal. Bus Duct is why going vertical has been so much more economic since WWII.
Posted By: Scott35 Re: Size feeder?? - 12/30/12 03:46 AM
Hey Sparkync,

I compiled a few Panel Schedules, per the spec's of the Project described in this Thread, and posted them as PDFs at the Technical Reference Area.

These items may be found under the Topic:
Example Panel Schedules - Per Thread at NEC Area.
*Note: Click the underlined text above to jump to that page.
Page will open in a new Tab or Window.

Per the Schedules:

Post Message #1 of 2 contains Schedules 1M and 2M.

"Panel: 1M" (Example #1) has the 208V 1 Phase 2 Wire Motor Loads' VA entries figured at:

a. 20 Amps x 208V = 4,160VA
4,160VA / 2 = 2,080VA per Phase.

and

b. 30 Amps x 208V = 6,240VA
6,240VA / 2 = 3,120VA per Phase.

-----------------------------------------------------------

"Panel: 2M" (Example #2) has the 208V 1 Phase 2 Wire Motor Loads' VA entries figured at:

a. 20 Amps x 120V = 2,400VA
2,400VA per Phase.

and

b. 30 Amps x 120V = 3,600VA
3,600VA per Phase.

--------------------------------------------------------
STATS FOR PANEL "1M":

Max. Load: 163.67 Amps on Phase "A", and 40.00 Amps on the Common Grounded Neutral Conductor.

% Volt Loss on the 25 Foot 3/0 THHN CU. Feeder is 0.32% L-L and 0.11% L-N.

SCA at the Panel = 10,435A - figuring:
10KA at the Distribution Panelboard (Feed Point),
1,830A Motor Contribution.

------ ------- ------ ------ ------ -------

STATS FOR PANEL "2M":

Max. Load: 185.00 Amps on Phase "A", and 40.00 Amps on the Common Grounded Neutral Conductor.

% Volt Loss on the 25 Foot 3/0 THHN CU. Feeder is 0.36% L-L and 0.11% L-N.

SCA at the Panel = 10,435A - figuring:
10KA at the Distribution Panelboard (Feed Point),
1,830A Motor Contribution.

-----------------------------------------------------

Schedules 1M and 2M have only the 1 Pole Loads designating the L-N Amperes / VA.
This is evedent in the lower tally fields, where the totals are shown per Phase and Neutral.

______________________________________________________________________________________________________________________

______________________________________________________________________________________________________________________

Per the Schedules:

Post Message #2 of 2 contains Schedules 3M and 4M.

"Panel: 3M" (Example #3) has the 208V 1 Phase 2 Wire Motor Loads' VA entries figured at:

a. 20 Amps x 208V = 4,160VA
4,160VA / 2 = 2,080VA per Phase.

and

b. 30 Amps x 208V = 6,240VA
6,240VA / 2 = 3,120VA per Phase.

-----------------------------------------------------------

"Panel: 4M" (Example #4) has the 208V 1 Phase 2 Wire Motor Loads' VA entries figured at:

a. 20 Amps x 120V = 2,400VA
2,400VA per Phase.

and

b. 30 Amps x 120V = 3,600VA
3,600VA per Phase.

--------------------------------------------------------
STATS FOR PANEL "3M":

Max. Load: 163.67 Amps on Phase "A", and 163.67 Amps on the Common Grounded Neutral Conductor.

% Volt Loss on the 25 Foot 3/0 THHN CU. Feeder is 0.32% L-L and 0.45% L-N.

SCA at the Panel = 10,435A - figuring:
10KA at the Distribution Panelboard (Feed Point),
1,830A Motor Contribution.

------ ------- ------ ------ ------ -------

STATS FOR PANEL "4M":

Max. Load: 185.00 Amps on Phase "A", and 185.00 Amps on the Common Grounded Neutral Conductor.

% Volt Loss on the 25 Foot 3/0 THHN CU. Feeder is 0.36% L-L and 0.51% L-N.

SCA at the Panel = 10,435A - figuring:
10KA at the Distribution Panelboard (Feed Point),
1,830A Motor Contribution.

-----------------------------------------------------

Schedules 3M and 4M have ALL Loads designating the L-N Amperes / VA.
This is evedent in the lower tally fields, where the totals are shown per Phase and Neutral.

Would like everyone to review these items and post comments.

TIA!

--Scott (EE)
Posted By: Scott35 Re: Size feeder?? - 01/05/13 10:54 AM
*** Follow-Up ***

Did the Values in these (4) Schedules make sense, or should I post more details?

--Scott (EE)
Posted By: harold endean Re: Size feeder?? - 01/10/13 03:41 AM
Speaking of feeder sizes, was this question asked before?

You can use #2 AL wire for a 100 amp service in a rsei install. If you use #2 AL for a feeder, you have drop the rating down to 9 amp. Right?

What about a generator? The wire from the generator to the transfer switch is #2 Al. So the generator OCP should be 100 amp? 90 amp?
Posted By: gfretwell Re: Size feeder?? - 01/10/13 06:42 AM
You can actually use #3cu for 100a if you can find it but the #2al is 90 like you say
Posted By: harold endean Re: Size feeder?? - 01/12/13 05:21 PM
Greg,

Do you know how many guys put #2 AL on 100 amp? Most of them.
Posted By: gfretwell Re: Size feeder?? - 01/12/13 05:44 PM
They would have some 'splainin to do with me.
90 is a standard breaker size so they can't round up.