Posted By: Niko 210.70(A)(3) lighting outlets - 03/25/09 04:18 AM
The way i interpret this section is if it has attic access it will sometime during the life of the dwelling the attic will be used as storage. So if i was the AHJ i would require to see a lighting outlet at any attic opening.

How would you interpret 210.70(A)(3) regardless if the attic has equipment.

Thanks for your thoughts.

Posted By: leland Re: 210.70(A)(3) lighting outlets - 03/25/09 05:21 AM
Not a chance.
4' of head room at the highest point. An 18"x18" opening in a closet ceiling. Hardly constitutes an attic,or storage area.

We will put crap where we will. I don't think this area fits the intent.

Now we move to 'intent'. I don't think any member of the CMP would try to store stuff there.
But then again...

Still not a chance. It will give them something to ponder,
Posted By: SteveFehr Re: 210.70(A)(3) lighting outlets - 03/25/09 05:40 PM
If the attic is accessible by means of a hatch, it's accessible for storage, and must be designed for it. Which means joists that meet load requirements, provision for proper insulation underneath the attic floor, light, etc. there should be at least one light there, with a switch accessible from the attic entrance, IMHO. Now, arguments can be made on this. If the attic is 12" deep in cellulose insulation and you can't even see the joists, letalone have a solid floor to stand on, I think you can make a pretty good argument that this attic is not suitable for storage. Not that the HO won't toss boxes up there anyhow, but eh.

As a homeowner, I'd sure like to see lights up there. In fact, I retrofitted lights in my own attic just so I wouldn't have to keep dragging flashlights up there; it's hard to walk around holding a flashlight when squatting, precariously balanced, on the 2x4s and sheets of plywood the previous owner and I tossed over the 12" thick insulation. Also, it's surprising how much weight you can put on a ductboard duct without collapsing it!

Posted By: gfretwell Re: 210.70(A)(3) lighting outlets - 03/25/09 06:56 PM
Florida 2009 update requires an attic access of a certain minimum size (22.5 x 30 I think) and a light, even in our 3:12 roofs with very low crawling around space.
They say if you can put a 24w x 42h box within the trusses it could be storage. The bottom chords have to be rated 20psf live load.

I put "jelly jars" with CFLs in my attic. They provide an extra level of protection from a bare bulb and won't burn you if you bump against them.