detached garage or structure disconnect?? - 10/21/08 07:54 AM
I have always been under the impression that a detached garage at a dwelling does not require a main disconnect at the garage eventhough it has a panel that has more than 6 branch breakers.
However, one of my students said that 225.32 applies.
but my defense was article 408.36 the main overcurrent device for a panel board can be located within or at any point on the supply side of the panel board.
The more I read 225.32 the more i agree with him that a main disconnect is required st the detached garage.
Please give me your comments.
Thanks.