Posted By: Yoopersup Bonding to cable tray - 03/11/08 10:42 PM
1 Inch inch conduit stubs up from mtr to under cable tray.
Cable trays grounded , Tray cable from tray to Conduit has equipment grounding conductor. Since cable tray is Not a raceway and Tray cable contains a equipment grounding conductor, Is a bonding bushing required and jumper from conduit to tray required.
YoopersUp
Posted By: JBD Re: Bonding to cable tray - 03/11/08 11:13 PM
Originally Posted by Yoopersup
1 Inch inch conduit stubs up from mtr to under cable tray.
Cable trays grounded , Tray cable from tray to Conduit has equipment grounding conductor. Since cable tray is Not a raceway and Tray cable contains a equipment grounding conductor, Is a bonding bushing required and jumper from conduit to tray required.
YoopersUp


Is your conduit connected to the tray at all? I have never recommended a bonding bushing and jumper if there is a clamped connection.
Posted By: Yoopersup Re: Bonding to cable tray - 03/28/08 02:08 PM
Mechincal connection in some cases , None in others.