Under the 2002 code is there a requirment for the ups to be able to disconnect commercial power if there is a fire?

If so what article?

Thanks

Windy
645.11
Remote EPO is only required for datacenters. For all other appliations, no remote is required, though certainly not prohibited. (Try convincing people that they need a magic "off" button without a code to point to, though!)