Posted By: JoeRossi MC Vs Conduit - 07/09/07 10:51 PM
Is mc concidered conduit?
Do you have an support one way or another?
Thanks for you help
Posted By: electure Re: MC Vs Conduit - 07/09/07 11:09 PM
Joe, MC cable is considered cable.
It must be supported and secured at intervals not over 6', and if 4 or fewer conductors #10 or smaller, must be secured within a foot of any fitting or termination.
Exceptions are where it's fished, or fixture whips up to 6' long.

See Article 330--especially 330.30
Posted By: teester Re: MC Vs Conduit - 07/22/07 10:01 PM
Ah, that dang NEC...