Posted By: barbwire Emt supports? - 07/06/07 01:02 AM
Hello all, I was told that on a vertical EMT pipe run you can support every 30 feet, but I cant find this in the code, is this true? Or does the 10 ft rule still apply?
Posted By: Luketrician Re: Emt supports? - 07/06/07 02:04 AM
The way I read it, 358.30(A) gives a general statement which covers this.

"EMT shall be securely fastened in place every 3m (10 ft)."

I could not find any other information though, I may be missing something here. There is an exeception to this if you are fishing a wall though.
Posted By: gfretwell Re: Emt supports? - 07/06/07 02:38 AM
Don't forget you also have to support the conductors if these risers get that tall.
Posted By: barbwire Re: Emt supports? - 07/06/07 08:05 PM
Thanks for the responce, I couldn't find anything either, 10 ft it is.
Posted By: Alan Nadon Re: Emt supports? - 07/07/07 03:21 PM
Greg mentioned conductor support it is located in section 300.19
Posted By: barbwire Re: Emt supports? - 07/07/07 03:33 PM
Yes, Thank you Guys, I referred to the table in 300.19, Thanks again.