Posted By: pbharvey multiple circuits feeding 1 rtu - 12/01/06 09:31 PM
Hi,
I'm an HVAC contractor and I have a job that has roof top units that are fed by two circuits; one for the heat pump compressor & fan, and a seperate circuit for the electric resistance heater. The unit I am replacing it with has a single point connection. I cannot get back to the panel. Can I run both circuits into a disconnect and come out of that into the RTU with a single feed? Thanks.
Posted By: iwire Re: multiple circuits feeding 1 rtu - 12/01/06 10:26 PM
No
Posted By: ShockMe77 Re: multiple circuits feeding 1 rtu - 12/02/06 12:09 AM
I think it's best if you contact a license electrician.
Posted By: gfretwell Re: multiple circuits feeding 1 rtu - 12/02/06 05:24 PM
It sounds like you don't have a unit that will work with the existing wiring. Call the manufacturer and see if they have a kit designed for that unit that will split the loads.