ECN Forum
Posted By:
lite bulb
what size parallel wire
-
10/06/06
10:31 PM
i am running a 1600 amp 120/208 volt 3ph service 300'underground, from a transformer to the building what size parallel wire is needed in alm.(and or in cu.)
Posted By:
Bob
Re: what size parallel wire
-
10/06/06
11:58 PM
4 #600 cu kcm per phase = 420 x 4 = 1680.
Posted By:
lite bulb
Re: what size parallel wire
-
10/07/06
01:34 AM
Is that 600mcm cu. allowing for the voltage drop in 300'.
Posted By:
Roger
Re: what size parallel wire
-
10/07/06
01:08 PM
Duplicate thread, please go to the link below.
https:/
/
www.electrical-contractor.net/
ubb/
Forum1/
HTML/
007648.html
Roger
©
ECN Electrical Forums