Posted By: Frank Cinker Non-Fusible Service Disconnects - 08/30/06 12:56 PM
Please give an example of where a non-fusible service disconnect can be used.

Thank you

[This message has been edited by Frank Cinker (edited 08-30-2006).]
Posted By: resqcapt19 Re: Non-Fusible Service Disconnects - 08/30/06 05:27 PM
Frank,
The only way you can do that is if you put the OCPD immediately adjacent thereto. 230.91
Don
Posted By: Alan Nadon Re: Non-Fusible Service Disconnects - 08/30/06 08:58 PM
As a "utility company" disconnect ahead of a meter socket it must be rated for service duty. They do not have OCP and are not the "service disconnect".
They are frequently used where a standard pull out meter socket is used for 480 V 3 phase, corner grounded, 200 amp or less on sewer lift stations. After the meter is the "service disconnect".
Bonding and grounding confusion with this kind of installation is extensive.
Alan--