Posted By: Sparks30 water main - 06/16/06 01:18 AM
It's been a while since I have done a 200 amp service, I'll be using 4/0 AL for service. #6 to ground rods. Does the water main get #4 ? Sorry to sound stupid just having one of those days.
Posted By: cpal Re: water main - 06/16/06 01:48 AM
6 for the ground is ok check 250.66
Posted By: Sparks30 Re: water main - 06/16/06 01:56 AM
250.66 says 4/0 AL with copper ground is #4. Or am I reading wrong?
Posted By: ShockMe77 Re: water main - 06/16/06 02:16 AM
#4 copper to the water main will be fine, and meets code per NEC.
Posted By: Sparks30 Re: water main - 06/16/06 02:29 AM
If I can run a #6 I will do that any wire I do not have to buy at these prices will help.
Posted By: gfretwell Re: water main - 06/16/06 02:37 AM
The ground rod conductor can be #6 but you still have to bond the pipe with #4.
Posted By: cpal Re: water main - 06/16/06 01:38 PM
oppps


I didn't catch the reference to the water pipe. Sorry

as gfretwell stated.
Interior water pipe requires a # 4 The rods are fine with the #6.


Sorry again


Charlie