Posted By: Ryan_J New SDS bonding requirement? - 11/09/04 12:48 AM
New section 250.104(D) seems a bit strange to me, but perhaps I am reading it wrong. The way I am reading it, it would be required to bond the closest metal water piping even if I am using the structural metal as the electrode. Likewise, if I am using the water pipe as my electrode, I have to bond the nearest structural metal. Does this seem strange to any one else? I mean, 250.50 already requires them to be bonded together, why the redundancy?
Posted By: iwire Re: New SDS bonding requirement? - 11/10/04 02:06 AM
It sounds very much like 2002 250.104(A)(4)
Posted By: Ryan_J Re: New SDS bonding requirement? - 11/10/04 02:36 PM
Interesting...I never even noticed that before shocked
Posted By: PCBelarge Re: New SDS bonding requirement? - 02/14/05 03:44 AM
Ryan
My understanding of this requirement is to keep the potential of the different systems in the area of the SDS as close to 0 as possible.