Replacement Luminaires / No Grounding Means - 11/06/04 02:57 PM
Quote
410.18(B) Made of Insulating Material
Luminaires (fixtures) directly wired or attached to outlets supplied by a wiring method that does not provide a ready means for grounding shall be made out of insulating material and shall have no exposed conductive parts.
Exception 2: Where no equipment grounding conductor exists at the outlet, replacement luminaires (fixtures) that are GFCI protected shall not be required to be connected to an equipment grounding conductor.
Luminaires (fixtures) directly wired or attached to outlets supplied by a wiring method that does not provide a ready means for grounding shall be made out of insulating material and shall have no exposed conductive parts.
Exception 2: Where no equipment grounding conductor exists at the outlet, replacement luminaires (fixtures) that are GFCI protected shall not be required to be connected to an equipment grounding conductor.