Posted By: George Little Stairways -Inside & Outside - 02/10/06 11:59 PM
What code would apply for a set of stairs on the exterior going to the second floor of a two family home? What would the artificial illumination requirements be? Along those same lines, if this set of stairs were to be on the exterior of a single family home where the stairs go into the basement? How about a set of stairs inside the attached garage where you have 6 risers to enter the house from the garage? Any 3-ways required?
Posted By: earlydean Re: Stairways -Inside & Outside - 02/11/06 02:18 AM
If your state or city has adopted the 2003 IRC:

"R303.6 Stairway illumination. All interior and exterior stairways shall be provided with a means to illuminate the stairs, including the landings and treads. Interior stairways shall be provided with an artificial light
source located in the immediate vicinity of each landing of the stairway. For interior stairs the artificial light sources shall be capable of illuminating treads and landings to levels not less than 1 foot-candles (11 lux) measured at the center of treads and landings. Exterior stairways shall be provided with an artificial light source located in the immediate vicinity of the top landing of the stairway. Exterior stairways providing access to a basement from the outside grade level shall be provided with an artificial light source located in the immediate vicinity of the bottom landing of the stairway.
Exception: An artificial light source is not required at the top and bottom landing, provided an artificial light source is located directly over each stairway section."

and:

"R303.6.1 Light activation. The control for activation of the required interior stairway lighting shall be accessible at the top and bottom of each stairway without traversing any steps. The illumination of exterior stairways shall be controlled from inside the dwelling unit.
Exception: Lights that are continuously illuminated or automatically controlled."
Posted By: George Little Re: Stairways -Inside & Outside - 02/11/06 03:17 AM
Thanks earlydean, I needed that info because I couldn't find anything in the NEC. We are on the MRC here in Michigan, which is just the IRC with the Michigan spin on it.
Posted By: e57 Re: Stairways -Inside & Outside - 02/16/06 09:16 AM
210-70?