I want to install three electric baseboard haaters on a 20 amp 240 volt circuit.The heaters are 1500 watt.The 240 volt circuit has 4800 watts.Do I have to use the 80% rule that limits me to 3840 watts?????? They will each have their own thermostat.I will be installing them in a motel.
Thanks bob
Based on 424.3 I would say yes.
If the supply is actually 208v, the heaters will run at 1300 watts, which total only a hair (60 w) over your 80% figure.
Larry:
Not to burst your bubble, but
208 volt, 20 amp equates to 4160 watts
80% equates to 3328 watts
1300 watts x 3 units equates to 3900 watts
Been there, done that
John
Sorry, Hotline...but your math is in error.
The heaters are not "constant amp load" heaters.
Here is how you calculate the expected load:
Assuming the heater nameplate says 240 volts, 1500 Watts. Using Ohm's Law, we find how many Ohms of resistance the heaters offer.
Now we look at the new voltage. Again using Ohm's law, we use the Ohms value, and divide 208 by that number. This will give us the amps at that voltage. Using that new amp number, we find our watts of demand.
Now, I'm just using "ballpark" math, but it looks like the heaters will put out less than 1200 watts at 208, which would allow you to comply with the 80% rule.
I'm really not sure that you can count on any of these calculations and suggest that you just check one at 208 if that's what you're going to use. I wouldn't expect the hot resistance of the element to be the same at 208 and 240VAC.
Joe
Okay, here's the real calculation (I hope):
1500 watts / 240 volts = 6.25 amps (at 240v)
240 volts / 6.25 amps = 38.4 ohms (constant)
208 volts / 38.4 ohms = 5.42 amps (at 208v)
3 x 5.42 amps = 16.26 amps (three heaters)
208 volts x 16.26 amps = 3382 watts (at 208v)
But the wattage is not important, the current is. 16.26 is a CH over the 80% of 20.
By the way, at 208 volts, 16 amps (80% of 20) is 3328 watts, so again, 3382 is slightly over.
I have a 240 volt SINGLE PHASE service.208 is a three phase wye.I have 240 volts 20 amp circuit 20 x 240 gives me 4800 watts.My question is do I have to knock this down to 80% x 4800 to 3840 watts?? I think it works this way.I have a 1500 watt heater 240 volts divide by 240 volts gives me 6.25 amps.times 1.25% would give me 7.8 amps for one 1500 watt heater. I'm going with two 1500 watt heaters that would be 15.6 amps four amps under 16 which is 80% of 20 amps.
Okay. What matters is the 3 x 6.25, which equals 18.75, exceeding 80%.
However, thermostatic heater controls cycle power, so the odds are that no heater will be powered for 3 hours (barring initial turn-on in freezing weather), not to mention all three being on for 3 hours.
So, you might have an argument against having a continuous over-80% load.
Guys George Little pointed out a code section that is right on target.
part of 424.3(B)
(B) Branch-Circuit Sizing. The ampacity of the branch-circuit conductors and the rating or setting of overcurrent protective devices supplying fixed electric space-heating equipment consisting of resistance elements with or without a motor shall not be less than 125 percent of the total load of the motors and the heaters.....
It does not matter if it is a continuous load or not, the branch circuit must be 125%
bobjobb,
You only need to derate the branch circuit or overstate the load by 25%, not both, as you indicated in your last post. 3 x 1500 watts equals 4500. 4500 watts @ 125% equals 5625 watts. At 240 volts, that would be a little less than 24 amps. Therefore, 2 circuits are required.
Approaching it from the reverse. How many feet of baseboard can be connected to a single 2 pole, 20 amp breaker? (250 watts per foot). 20 amps at 80% equals 16 amps. 16 amps times 240 volts equals 3840 watts. Divide that by 250 watts and you get 15 feet of baseboard per 20 amp circuit breaker. (a useful number to remember).
Could your job get by on 3 five foot baseboard heaters rather than 3 six footers?
Or run a 30-amp circuit, if permissable. Can you re-pull the circuit? If not, running a new one can't be much easier.
I agree with everyone who says this is a code violation but I also agree it is only a 250 milliamp violation. You could confirm that by verifying the 208 draw is ~1133w from the manufacturer.
You really need that data to make an informed decision ... or a clamp on.
If it really is 16a and a CH I doubt I would make them rip out drywall. I would use 310.16 to let me sleep
edit
I just looked at the Broan site and some of their toaster wire heaters. They confirm that a 1500w heater @ 240v pulling 6.25a is a 1125w heater pulling 5.41a @ 208
[This message has been edited by gfretwell (edited 02-04-2006).]