Posted By: GamecockEE Assembly Location Methods - 10/24/05 03:38 PM
Looking at a small restaurant which the architect has classified as a type V-B, which seems to indicate a non-rated fire construction according to 518.4(B). Is type NM cable allowed providing the walls & ceilings have at least a 15 min fire rating as per 334.10(3)?
Posted By: macmikeman Re: Assembly Location Methods - 10/24/05 05:06 PM
I would ask the AHJ for my area if it is ok with them before starting to wire. Just to be on the safe side. Now here is my personal take. Rats like to eat at resturants. And they like the sheath and insulation of romex cable for desert. I use mc or emt when I wire resturants even if I could use romex for that simple reason.
Posted By: Ryan_J Re: Assembly Location Methods - 10/24/05 06:14 PM
NM cable would be permitted.
Posted By: DougW Re: Assembly Location Methods - 10/26/05 09:45 PM
I'd think it would be OK, but I'd still check with the AHJ - some frown on NM in commercial occupancies, even when they allow it for resi.
Posted By: Ryan_J Re: Assembly Location Methods - 10/26/05 10:06 PM
I wouldn't care if they frowned or not. Unless there was a legally adopted amendment to the code, I would use it. [Linked Image]