Says, they must be grouped, and access to occupants... Seems they only need to able to shut off thier own alone, but need to be grouped together in the same general area.
230.72 Grouping of Disconnects.
(A) General. The two to six disconnects as permitted in 230.71 shall be grouped. Each disconnect shall be marked to indicate the load served.
(B) Not applicable...
(C) Access to Occupants. In a multiple-occupancy building, each occupant shall have access to the occupant’s service disconnecting means.
Exception: In a multiple-occupancy building where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the service disconnecting means supplying more than one occupancy shall be permitted to be accessible to authorized management personnel only.
Commentary:
A multiple-occupancy building may have any number of dwelling units, offices, and the like that are independent of each other. Unless electric service and maintenance are provided by and under continuous supervision of the building management, the occupants of a multiple-occupancy building must have ready access to their disconnecting means as required by 240.24(B).
I also don't think this situation is applicable to the exceptions in 230.40... They aren't of different characteristics(#1), not grouped in one location(#2), not a single family dwelling with seperate structure(#3), for common area branch circuits(4), or covered by 230.82(4) or (5), in exception (#5).