Posted By: Dougaphs Bath Fan - 03/08/05 02:22 PM
What is the current requirements on bath fan and Code Reference number?

I am under the assumption that Bath Fans are required even if you have a window, is this not correct?

Similar, what are the requirements for kitchen exhaust fans and Code Reference number?

I am wanting to add General electrical notes to drawings.

Thanks in advance
Posted By: gfretwell Re: Bath Fan - 03/10/05 01:21 AM
The Florida Building Code (based on the IRC) 1203.4.2 says every toilet room shall have a 3 sq/foot window OR mechanical ventilation.
Posted By: Ryan_J Re: Bath Fan - 03/10/05 02:22 PM
IRC R303.3 and its exception require 1.5 sqaure feet of opening or an exhaust fan.
Posted By: Dougaphs Re: Bath Fan - 03/10/05 11:10 PM
Ryan,

Thank you for the info. I really appreciate it.

Doug
Posted By: Ryan_J Re: Bath Fan - 03/10/05 11:37 PM
Your very welcome.