Posted By: Bill Addiss Panel Under Tub - 10/27/03 03:17 PM
[Linked Image]

What does the Building Code(s) have to say about this?

This house was probably 30+ years old and this wall was opened during a Kitchen renovation. I was told all of the homes in the development were like this.

If an Inspector was here now to inspect some new rough-in items would he, or could he say anything about the trap being over the panel, or that the panel (other side of wall) is now in a Bathroom?

Bill
Posted By: PCBelarge Re: Panel Under Tub - 10/28/03 08:55 PM
This is an excellent example.
I will give you my [Linked Image] interpretation, This is not too uncommon and in this installation I think it is permitted. Water can leak down from most anywhere above a panel and if we had to worry about bathrooms/kitchens or any sinks, it would limit us in a lot of dwellings.

Pierre
Posted By: Bill Addiss Re: Panel Under Tub - 10/28/03 09:38 PM
does a Plumbing trap have to be accessible?

In this case it will be sealed up in the wall again when the room is finished.

Bill
Posted By: Ryan_J Re: Panel Under Tub - 10/28/03 11:58 PM
Those particular types of fittings are called "slip-joint", and yes they must be accessible. Not all traps need to be accessible, just slip-joints.
Posted By: Roger Re: Panel Under Tub - 10/31/03 02:25 AM
Back to the electrical part of the installation. Now that the wall is open, wouldn't most inspectors require proper supporting of the NM?

Roger
Posted By: ga.sparky56 Re: Panel Under Tub - 10/31/03 02:58 AM
Hi Roger, The ahj's I've dealt with in your state certainly would.

Russell