Tim,
Nice find there
I see what you're referring to as far as the slots not being aligned straight... but my guess would be it was intended to function at the outlets I posted earlier... As far as what that function would be, I'm guessing code wise, they weren't too particular about a 120V plug fitting a 240V outlet & vice versa.. & these outlets could be used for either! Is there any markings on this regarding manufacturer, ratings, etc?
Rob,
Even though you don't have a 2 pole breaker for the outlet, doesn't mean someone didn't connect it to both phases via 2 - 120V circuits someplace.. I'd test it with a meter to see what voltage is present..
The left outlet in the pic I posted is labeled "Magnus" "10A 250V" on the face.. but it was connected to 120V (the original service that I changed out was 30A 120V in that house!) Under a window in the baseboard, I'd make a wild assumption that it was an original general use outlet, since the baseboard is where they seemed to put all the outlets back in these days.. As far as for an A/C unit... I'd bet the extinction of this outlet style was likely some time before A/C was around...
Matt E.
We quite frequently use Nema 5-15 outlets rated for 15A 120V on circuits using 20A breakers.. Code allows this as long as there are more than 1 outlet.. (A duplex satisfies this) If you're only installing one single outlet on a 20A 120V circuit.. It must be Nema 5-20 per NEC 210.21(B)(1)
I'd love to get my hands on a wiring guide or some type of electrical code book from back in the era this stuff came from.. To think the code book back then was probably no thicker than an average magazine!