Posted By: BigJohn Permitted Hot Work - 03/17/07 06:00 PM
The company I work for has just adopted 70E which we're all being tested on. We've gotten a couple of catagory 2 and catagory 4 blast suits with the insulated gloves and sheilds and such.

Originally everyone worked hot without any protection, and now we at least have these suits, so this is a step in the right direction. But the attitude that they've created seems to be something along the lines of "now that we have these suits, we never have to worry about attempting to shut down."

I've heard (mostly on here and other message boards) that OSHA prohibits any work that by defintion doesn't have to be preformed hot (i.e.: anything other than voltage and power testing, etc.) I said this and was told that while I was prohibited from working hot, licensed electricians certainly could.

Both NFPA 70E and CFR 1910 Subsection S seem to say the same thing: "Live parts to which an employee may be exposed shall be deenergized before the employee works on or near them, unless the employer can demonstrate that deenergizing introduces additional or increased hazards or is infeasible due to equipment design or operational limitations."

That doesn't read to me like a prohibition of hot work. That reads to me like a massive loophole to allow hot work. It seems like it just leaves it at the discression of the electrician to decided whether or not shut-down is feasable. If knocking out a lighting circuit puts a group of people in the dark, has that created additional hazards? Is shutdown infeasable because of the lighting circuit layout?

Yes or no, can we or can we not work things hot? This doesn't seem very clear cut at all.

-John
Posted By: resqcapt19 Re: Permitted Hot Work - 03/17/07 09:21 PM
John,
It is not really that big of a loophole. The notes to 1910.333(a)(1) say:
Quote
Note 1: Examples of increased or additional hazards include interruption of life support equipment, deactivation of emergency alarm systems, shutdown of hazardous location ventilation equipment, or removal of illumination for an area.

Note 2: Examples of work that may be performed on or near energized circuit parts because of infeasibility due to equipment design or operational limitations include testing of electric circuits that can only be performed with the circuit energized and work on circuits that form an integral part of a continuous industrial process in a chemical plant that would otherwise need to be completely shut down in order to permit work on one circuit or piece of equipment.
Also look at this letter of interpretation.
Don
Posted By: BigJohn Re: Permitted Hot Work - 03/17/07 09:49 PM
That letter of interpretation says that unless an additional hazard can be demonstrated to be cause by denergizing, then everything has to be shut down.

That only addresses one of the conditions under which we are apparently allowed to work hot. The other condition is Note 2 which concerns whether or not it is "feasable" to shut down the equipment due to design considerations. This is the part that seems like the loop-hole.

Where do you draw the line between interrupting industrial processes and shutting off a circuit controlling a couple of personal computers? How much inconvenience is tolerable before something becomes "infeasable"?

This may seem argumentative, but I'm trying to get a clear answer because these are the arguments I'm going to get if I use NFPA 70E to suggest that we shouldn't work everything hot simply because we have a flash suit.

-John
Posted By: renosteinke Re: Permitted Hot Work - 03/17/07 11:37 PM
My biggest problem with these regulations is that they muddy the waters as to who gets to make the call.

IMO, we, as professionals, are the final authority. Period. WE decide - yes or no.

Throw a new regulation into the mix, and there's all sorts of other folks ... supervisors, managers, engineers, Personnel wonks, chairborne commandos ... who suddenly feel that they get to make your decision for you. "What's the problem? We got you a suit- go ahead and work hot." Or, the opposite: "Joe did it hot yesterday, what's the problem?" Then there's always the Nimrod who wants to write a guy up for not wearing safety glasses while he washes his face...

If the place thinks the line workers are simply chimps with tool belts, then no amount of regulation will fix a management made up of banana-brains.
Posted By: Mark20 Re: Permitted Hot Work - 03/18/07 07:39 PM
i started with a new company last year and on my first day i had to read and sign paperwork about an inch thick pertaining to safety rules that everyone is supposed to follow. thing is i soon realized that the job foremen don't enforce these rules at all. if everyone looks the other way it sends a message "don't worry about it". then if you do want to do things the safe way let's face it,it takes you longer to do the same job as the guy who's cutting corners. being new to the company i didn't want to "make waves" so i did everything like everyone else. my ?? is by signing that paperwork are they going to be obligated to pay workman's comp if someone does get hurt cutting corners. (e.g. working off a step ladder that's leaning against the wall because you don't have room to lock the spreaders and we don't have straight ladders on site or not being tied off when working near a leading edge elevated above 6ft.) in my first month i worked a saturday when we were trying to make a deadline and i was sent into a bathroom to fix 277v recess cans that wouldn't come on, (new construction, unoccupied) i asked the subforeman to turn off the curcuit and he said "the boss (foreman) said f#@% it work 'em hot. well, the guy who wired 'em wrong the first time didn't wire 'em hot -or- correctly for that matter. of coarse i did as told and cussed under my breath the whole time. again my ?? is how much legal responsibility does the company have if i would get hurt? how many loopholes do you think their lawyers can find to prtect their pocketbook? any opinions on this would be appreciated.
Posted By: Luketrician Re: Permitted Hot Work - 03/18/07 08:51 PM
Hi Mark, for the example you gave of your 277V lighting issue, I pose this question and comment. Isn't working on energized equipment part of the trade? I will always work between grounds, and de-energize when possible. I surley do not feel the need to 'show boat' by working equipment 'hot' when there is no need too. I definitely don't disagree with your beliefs and convictions on the topic..BTW

I also belive that some formen...some.. forget over time how dangerous and unforgiving it is working on energized equipment. They spend to much time in the office and mulling over prints. Maybe the formen you mentioned 'fits the bill'. How long would it have took you to go and flip the breaker for that circuit anyway? Was it feeding something else besides the bathroom? Seems that maybe you could have broken a tap to de-energize without the boss knowing possibly? Just an idea...good luck out there!

Luke
Posted By: Mark20 Re: Permitted Hot Work - 03/19/07 09:50 PM
luke, thanks for the reply. i have worked on plenty of hot circuits myself. in fact when i used to be a licensed journeyman hvac repairman it seems i worked on stuff hot even more often than i do now as a master electrician (troubleshooting problems on a daily basis). so i'm not a stranger to it. and yeah, once i found where the circuit was fed at i did kill it at a splice as you suggested. i was new on the job and had no idea where the breaker was to turn it off (this was a big fed gov't building)- that's why i kindly asked my subforeman to do it. i did get shocked that day re-making that splice (5 12-2 mc's is kind of hard to splice together even when it isn't hot) not bad though, just enough to upset me. i learned a lesson that day, don't take no for an answer. i've been with the company over a year now and have stood my ground more times than not. seems people respect that. i'm a subforeman myself now.
Posted By: Luketrician Re: Permitted Hot Work - 03/21/07 12:03 AM
Sorry Mark20, I didn't realize that you were a Master electrician. I'm just a j-man myself. You probably have forgot more than I will ever know, (along with many others on this site) but I am still learning. smile
Posted By: greco Re: Permitted Hot Work - 03/21/07 01:02 AM
John,
Unfortinately its hard to get a yes or no anwser to questions from OHSA. In my opinion should there be an accident your company will have to justify why things were not shut down. If your employer thinks about it that way it may be eaiser to get a shut down. Also a short circuit may cause longer down time than a short outage or moving to a temporary source.
It is also my opinion that that ppe is no substitute for a shut down. Remember your safety is most important to you. If you do not feel comfortable with the task don't do it. I would rather find a new job that valued my safety and judgement. I know thats easy for me to say so take care of yourself out there.
Jeff
Posted By: renosteinke Re: Permitted Hot Work - 03/21/07 02:30 AM
Mention PPE and some strange attitudes form. I look at PPE the same way I look at parachutes:

If the plane is working fine, in a quiet environment, it's nice to know it's there if you need it - and silly to wear it.

If you know you're entering a high risk environment, by all means, don it 'just in case.'

If you have a choice - to jump, or land with the plane - by all means, land with the plane. (This equates to turning off the juice whenever possible).

If you absolutely must jump, by all means use the parachute! (If you must work hot, take every precaution you can!)
Posted By: Trumpy Re: Permitted Hot Work - 03/22/07 07:35 AM
Let me get this straight.
You get a suit that may prevent an Arc blast harming you and all of a sudden it's OK to work live?.
If your boss or foreman requires that you work hot when they aren't there to assess the situation,get them to come to the site and do it themselves.
And, do they require you to work by yourself?.
Get this, under company policy here, it is a dismissable offence to require any worker to work with live conductors or isolators where it is not possible to de-energise such equipment or lines.
Every person that is working on a live installation or works shall have 2 helpers (being suitably qualified) and a Safety Observer.
PPE or no PPE, just be very aware that your actions (or in-actions) can have serious results.
Posted By: Zog Re: Permitted Hot Work - 03/23/07 03:01 PM
The funny thing about the 70E is that it states in 110.8 to not do any energized work and is followed by about 30 pages of how to work on energized equipment.

Working hot because it is easier is not allowed. The term feasable according to websters is "Capable of beaing done, possible" is shutting down the equipment and placing it in an electrically safe working condition (LOTO, voltage check, grounded) possible? Thats the question you should be asking your self.
Posted By: BigJohn Re: Permitted Hot Work - 03/25/07 09:00 PM
From what I've read here, it seems like there isn't any clear-cut answer like I was hoping for.

I really think OSHA weaseled with that second statement that allows hot work when shut-down isn't "feasable". Seems like they had it right when they said hot-work was only permissable when it created additional hazards. That would at least make enforcement easier.
Quote
Let me get this straight. You get a suit that may prevent an Arc blast harming you and all of a sudden it's OK to work live?.
That is exactly how a lot of these guys interpret it.

I said it in another thread on this site but it bears repeating: The problem in this trade is that there is an actual hostility towards safe-work practices. I own all the PPE required for class 1 and 2 hot work. I can't even get guys I'm working with to use insulated tools when they do things hot, even when I offer them, they'll refuse and keep on using their uninsulated ones. How much sense does that make?
Quote
...Should there be an accident your company will have to justify why things were not shut down. If your employer thinks about it that way it may be eaiser to get a shut down. Also a short circuit may cause longer down time than a short outage or moving to a temporary source.
I agree 100%, unfortinately, no one thinks it will ever happen until it actually does.
Quote
If you do not feel comfortable with the task don't do it.
I have refused to work some things hot, and I will continue to as necessary.

Thanks for the replies.

-John
Posted By: Trumpy Re: Permitted Hot Work - 04/05/07 10:21 AM
John, you can argue until you are blue in the face.
Until someone gets hurt or seriously burned, it's a doddle working live.
It's unreal how many clowns we have in this trade.
Posted By: ayrton Re: Permitted Hot Work - 04/26/07 08:06 PM
How many of you in the field have ever had serious arc flash burn?

IMO this is one big reason people will work hot. They havent been burned.

99% of the time you should be able to de energize what you are working on. Period

Yes people may be inconveinienced but Big deal. I would rather someone be inconvenienced than me or my people be put in unecessary danger.

This has been a hot topic for us as of recent for I was burned with arc flash last November, my brother was last Friday, and a maintenance man at one of my customers building was almost cut in half by a breaker that let go.

If you tell your boss you wont work on that particuliar item hot, let him fire you. He would be in a heap of trouble and he knows it!

A simple thing as resetting a tripped breaker can kill you. May take one in a thousand for it to happen, but it could.
Posted By: ayrton Re: Permitted Hot Work - 04/26/07 08:08 PM
PS I made this post reply with out seeing Trumpy's remarks. Right on Trumpy you are dead on