Transformers & Feeders: 3 Phase 4 Wire Wye - 03/19/10 12:59 PM
Transformers & Feeders: 3 Phase 4 Wire Wye
Five Drawings of Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus OCPDs and Panelboards for:
3 Phase 4 Wire Wye Transformers
(Two Voltage SDS)
NOTE: Click on Image to view Full-Sized Image
----------------------------------------------------------
Drawing 3PH4WY-1: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary OCPD at Panelboard.
-----------------------------------------------------------
Drawing 3PH4WY-2: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders, Additional Panelboard "Subfed".
Secondary OCPD at First Panelboard.
-----------------------------------------------------------
Drawing 3PH4WY-3: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Two Panelboards fed via Tapped Feeder.
Secondary OCPD at each Panelboard.
-----------------------------------------------------------
Drawing 3PH4WY-4: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Two separate Panelboards fed by Secondary Feeders- each set derived from "X" Terminals.
Secondary OCPD at each Panelboard.
-----------------------------------------------------------
Drawing 3PH4WY-5: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Distribution Panel fed by Secondary Feeders.
With Secondary OCPD at Distribution Panel.
-----------------------------------------------------------
Text #3: Two Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)
-----------------------------------------------------------