Posted By: Schiebs4 LOTO and working on live equipement - 11/08/00 08:44 PM
I am setting up a LOTO program. A question of when is it appropriate for craft electrician to work on live equipment? What are the allowable situations?
Posted By: Wrradd Re: LOTO and working on live equipement - 11/09/00 12:00 AM
What is a LOTO program?
My personal opinion is; There is no situation, or condition, that requires a system, or equipment, to be worked while it is energized. Electing to do so, is a personal choice, of the individual. OSHA rules forbid working a live system. There is always alternatives.
Posted By: Bill Addiss Re: LOTO and working on live equipement - 11/10/00 12:54 PM
That is a question that may not have a specific answer. Even though, in practice, many tasks are often carried out "Live", as Bennie says, it is usually out of convenience not necessity. How can you tell someone that it is acceptable to risk Injury or worse?

Even using myself as a example, there are times that I will work on an energized system, and times I will not. It is not always for the same reason. Sometimes, I will just not feel comfortable doing it live that day and will request a shut down - even though it may be a task I have performed many times in identical situations. I feel that working live requires a cool head, a steady hand and a degree of concentration. When one of those is out of place, I usually just won't do it. That is what causes accidents.

I would like to see more opinions on this.
Posted By: resqcapt19 Re: LOTO and working on live equipement - 11/10/00 04:12 PM
OSHA allows only very limited wotk on live equipment. Troubleshooting is the most common reason to work equipment live. There are very few others and they involve equipment where the deenergization of the equipment would introduce more serious safety hazards. Some chemical processes fall into this catagory. Even when OSHA permits work on "hot" equipment, special PPE (personal protective equipment) is required. 1000 volt rated tools and gloves is the minimum. If the energy level is high then much more is required, up to and including full head covering with flash protective lens and full insulated nomex (or other flame resistant) outer clothing. Non-electrically qualified people can not be within 3'6" of any exposed energized electrial equipment of any voltage above 50 and less than 750 volts.

These rules have been in OSHA for at least 10 years and the industry is just now starting to follow them. Also look at NFPA 70E, Standard for Electrical Safety Requirements for Employee Workplaces.

LOTO= lock out/tag out
Posted By: Scott35 Re: LOTO and working on live equipement - 11/10/00 07:32 PM
Quote
Originally posted by Bill Addiss:
That is a question that may not have a specific answer. Even though, in practice, many tasks are often carried out "Live", as Bennie says, it is usually out of convenience not necessity. How can you tell someone that it is acceptable to risk Injury or worse?

Even using myself as a example, there are times that I will work on an energized system, and times I will not. It is not always for the same reason. Sometimes, I will just not feel comfortable doing it live that day and will request a shut down - even though it may be a task I have performed many times in identical situations. I feel that working live requires a cool head, a steady hand and a degree of concentration. When one of those is out of place, I usually just won't do it. That is what causes accidents.

I would like to see more opinions on this.

Bill;
You took the words right out of my mouth, more like my fingers [Linked Image]. Everyone in the trade knows how that feels to be a little "Off The Norm" on a project, usually brought on by what happened on the way to the job that morning [cut off by some clown on the freeway and nearly had an accident, lost wallet, etc.]. That's definitely not the time to work on a hot 480 v 3 phase 3 wire corner grounded Delta subpanel [or any other panels and/or system voltage].
What's funny is that I didn't know that too many other people felt this way, as a lot of the contractors that I had worked for when I was in my twenties would go balistic and call you a pansy if you didn't feel completely secure that day to dive into live switchgear and land those subfeed breakers!! Luckilly, since the early 1990's, I have been fortunate enough to be in the position where I don't need to work for another Electrical Subcontractor, so the whole working on hot equipment situation has completely changed and I will only work on live equipment if it just cannot be shut down without causing problems. If so, none of the guys working for or with me will be required to work the hot gear [I will do it], unless I absolutely need someone elses help.
Went through enough headaches and BS on the job when I was a kid to know it sucks! Damned if I'll turn around and make someone else do it now!

To sum up this message; You, Bennie and Don have said a mouthful in relatively few words. Very few situations call for working on hot equipment, but where [or when] it is considered to be Allowable Situations - as far as OSHA is considered - is unknown to me, other than with proper protective gear + proper training for the type system; to diagnose system performances and troubleshoot, or if the location cannot be powered down without some major catastrophy occuring.
I personally would like a LOTO program and devices to be as "Idiot Proof" as possible, having been the sorry victim of a determined moron turning on breakers because they wanted to use the copier so bad and couldn't wait another 10 minutes, then to find out that the copier's power switch was turned off and that's why it wasn't working.. not because the breaker I had tagged / locked off in the 277 volt panel was feeding it [sounds stupid, but it happened and BOY I was PISSED !!]

I'll go back to my room now [Linked Image]

Scott "S.E.T."
Posted By: Vin Re: LOTO and working on live equipement - 11/10/00 09:56 PM
Another reason to work live would be for life support systems. Also, if shutting the power to the circuit leaves a work area in the dark it would be permissible to work live. The osha standard you're talking about is 1910.333 The industrial facility where I work has all the panel boxes and disconnects retrofitted with lockable access panels for the very reason Scott mentioned. I know this is an electrical site but just in case someone doesn't know: to be locked-out tagged-out the equipment must be at zero energy potential meaning electrical,hydraulic,pneumatic, steam,etc. One thing to add,if starting a LOTO program, remember to tell your employees the obvious which is to "try" the equipment when it's locked-out.
Posted By: doc Re: LOTO and working on live equipement - 11/25/00 05:40 PM
ok someone help me here there is a article in the NEC code on working on live parts but is for testing only.
Now if you are serious about a LOTO system then you have to be trained in it before teaching others ,you must have a complete commitment from upper management for this to work and you have to be prepared to either walk out the door and call the proper legal authorities if the rules are broken by upper management,if you don't then you are wasting your time .YOU cannot have a part time loto system it is more dangerous than none at all in my opinion. With a loto system still do not assume that the power is off make this part of your rules { AFTER TURNING OFF AND LOCKING OUT YOU MUST STILL TEST CIRCUIT WITH METER BEFORE WORK CAN BEGIN,NOT DOING THIS IS SUBJECT TO DISCIP. ACTION. Last remember no one can remove the lock except the person that puts it on or someone willing to take responsibility for any harm to persons or equipment
Posted By: resqcapt19 Re: LOTO and working on live equipement - 11/26/00 02:29 AM
Doc,
Not only must you test the equipment for voltage after you have locked it out, you must also verify that the test equipment is in working order before and AFTER you have tested the voltage at the equipment that has been locked out.
Don(resqcapt19)
Don has made a very good statement. The SOP of a circuit, or high voltage line clearance, is to test "live", and then test when "dead". The live test, tests the tester, also retest tester after clearance.
I once, had the blades of a disconnect, separate from the operating shaft. I pulled the handle and locked it with a padlock. The circuit was still live. There is occurrences of one, or more, blades not being disengaged. The test procedure should follow accepted methods.
Posted By: LNP&S Re: LOTO and working on live equipement - 01/05/01 11:57 AM
Bennie
Strange that I should read your post relative to a "disconnected disconnect" today. Ran into something very similar just yesterday. An older facility with a dry sprinkler system in a sub-basement. There was an old 2 pole fused disconnect for the 115 v air compressor used to maintain system pressure. The other side of the disconnect was used to power a make shift 115v alarm system connected to the system. The installer had cleaverly disconnected the linkage between the two sets of blades so the compressor could be disconnected without disabling that alarm system. Cleaver if not Kosher.
Posted By: sparky Re: LOTO and working on live equipement - 01/05/01 09:01 PM
Bill, you could make $$ writing for someone.
Scott, my brother, also a Sparky, actually had some bonehead cut a lock off a disco! [Linked Image]I carry basic L.O.T.O. , I do believe that OSHA addresses "employees". And as no one can put up with me, I believe I am exempted. [Linked Image]
I believe that "safe" is a relative term.
[Linked Image] [Linked Image] [Linked Image]
Posted By: Bill Addiss Re: LOTO and working on live equipement - 01/08/01 11:50 PM
Sparky,

So you will buy my book?
(just kidding)
This is quite a problem with our trade.
We are very often expected to work live and under (much) less than perfect conditions.
And, unfortunately We cannot exclude the "Boneheads" from joining the trade.
Posted By: sparky Re: LOTO and working on live equipement - 01/09/01 11:31 PM
So true Bill....ya know, i wonder how things like this would sugar off if the local AHJ had a "bonehead-of-the-month" award. I bectha they got a few contestants in mind... [Linked Image]

[This message has been edited by sparky (edited 01-09-2001).]
Posted By: doc Re: LOTO and working on live equipement - 01/10/01 03:24 AM
Just a few months back I installed a 800 amp fused disconnect and 2 200 amp disconnects all 4 pieces were brand new also installed a 800 amp breaker panel.All of this was by the same MFG. not one of the disconnects would disengage all 3 blades the 800 amp none of the blades pulled and the 200s had 1 or 2 blades that stayed engaged the main breaker in the panel when turned off one leg stayed hot.The MFG. of the equipment sent a person out to install complete new panels and disconnects and no they were not federal brand
Posted By: Scott35 Re: LOTO and working on live equipement - 01/10/01 03:43 AM
The AHJs could have their own version of "America's Most Wanted" [Linked Image]

For the Tradespersons, how about posting the "Boneheads'" picture in Wholesale Houses [suppliers] all over the country, much like FBI has pictures of wanted people in the post offices.. [Linked Image]

I have seen a few clowns, but thankfully they are few and far between [Linked Image]

Scott.
Another incident regarding properly testing after opening the breaker was; The panel was a 480 three phase supplying four welder outlets. The was one spare breaker. I shut of breaker No.#1 marked plainly to match outlet No. #1.
I tested one phase to ground, it was dead. I disassembled the front part of the arctight
receptacle and was hit by 277 volts on one phase. Checking the breakers revealed the reason. When the panel was originally connected it was one space off with all three wire terminations. The top breaker had an empty space and the last breaker had one pole connected. This had been in operation for many years.
Lesson learned, test all three phases, to ground and to each other.
Posted By: Schiebs4 Re: LOTO and working on live equipement - 01/10/01 01:26 PM
Gentalman,

I would like to thank you for all of your responses. In our LOTO program, and Electircal safety Program I will be takeing several of your suggesions and making sure that my workers are taking the precautions.
[Linked Image]

I would like to pose another question for you, Would you require people to wear hard hat, face shield to work open a panel that only contains a 110V line located at the very top feeding power to 24V conections that operate selenoids for air lines?
Posted By: Vin Re: LOTO and working on live equipement - 01/11/01 12:34 AM
If the air lines were close by and by turning the power off the solenoids would realease 90psi of air that could send a projectile in your face, then yes, I would recommend this PPE. If this was SOP at the facility and you signed off that you read and understood their safety policy and one of your employees got hurt you could be held liable for a willful violation.
Posted By: Bill Addiss Re: LOTO and working on live equipement - 01/11/01 07:41 AM
You have to keep the higher voltage in mind when thinking about safety and precautions. Any procedures or standards that you set in your program should take existing conditions into consideration - such as Working Clearances, Proper lighting, condition of tools etc. These can greatly affect the overall level of safety in even the simplest of procedures.
Posted By: Bgame Re: LOTO and working on live equipement - 01/12/01 04:46 AM
ONE OTHER THING THAT MUST BE TAKEN INTO ACCOUNT AS FAR AS LOTO GOES-IN AN INDUSTRIAL SETTING ANYWAY-IS THOSE PESKY OPERATORS. I'VE BEEN AN INDUSTRIAL ELECTRICIAN FOR SOME TIME NOW AND THE ONE THING THAT HAS BEEN A CONSTANT IN EVERY PLACE THAT I HAVE WORKED IS THE WILLINGNESS OF SOMEONE TO START A MACHINE OR SYSTEM WHILE I AM WORKING ON IT.

LOCK IT OUT.