Posted By: Bob Hinshaw 10 amp circuit breakers - 02/20/02 02:01 PM
I have a friend who was asking me about a problem he is having in his house. He keeps tripping 10 amp circuit breakers, especially on the freezer and micro wave circuit. First, I didn't know it was acceptable, especially in a newer home, to use 10 amp breakers. I cannot find in the code where it states that you can and what wire size to use. Is this acceptable, or should the breakers be changed, if the wire size is correct?
Posted By: CTwireman Re: 10 amp circuit breakers - 02/20/02 04:51 PM
10 amp breakers? [Linked Image] That's a new one on me!! Could you give us some more information? Like the manufacturer and model # of the breakers and panel?

Are you sure that the writing hasnt worn off on the breaker and you are misreading it?
Posted By: Redsy Re: 10 amp circuit breakers - 02/20/02 05:00 PM
I believe some manufacturers make "unit breakers" to be individually mounted on a din rail or similar application, to protect specific piece of equipment. However, for branch ckts., 210.3 shows a minimum rating of 15 amps. Also, I don't believe UL lists branch circuit breakers below 15 amps

[This message has been edited by Redsy (edited 02-20-2002).]
Posted By: WARREN1 Re: 10 amp circuit breakers - 02/20/02 05:50 PM
You are right Redsy. Square D makes a QOU unit mount miniature breaker as low as 10 amps in 120/240 volts 1,2,3poles and 277 volts 1pole.
Art. 240-6 of the 1999 NEC list only as low as 15 amps, but the next sentence says non-standard fuses and inverse time breakers shall be permitted.
Posted By: sparky66wv Re: 10 amp circuit breakers - 02/20/02 05:50 PM
Square D and other breakers have a large #10 on the face, which means 10,000 Amps Interrupting Current, not 10A Overcurrent protection.

Look closer at the black numbers on the toggle itself if Sq D, or near there...

It should say either 15, 20, (or God forbid) 30 on it...
Posted By: Bob Hinshaw Re: 10 amp circuit breakers - 02/20/02 07:09 PM
Thank you guys for your quick response to my inquiry. I have sent these responses to my friend who is going to double check his panel tonight. I am hoping it is what sparky66wv suggested. Will keep everyone posted.
Posted By: Bob Hinshaw Re: 10 amp circuit breakers - 02/21/02 01:51 PM
After further investigation, he discovered it was a 15 amp circuit breaker, with the large #10 on it. Well, he still has a problem, but I feel better. Thank you guys for your help.
Posted By: JBD Re: 10 amp circuit breakers - 02/21/02 01:53 PM
10 amp breakers are common in industrial control panels. Square D makes a QO plug-on and QOB bolt-on panel style in 1, 2, and 3 pole versions as well as their unit mount QOU. (Look at page 8-10 in their Digest).

These are not common in normal panels or loadcenters.
Posted By: Bill Addiss Re: 10 amp circuit breakers - 02/21/02 03:20 PM
Bob,

Does He have a Microwave over the Stove?
Just a guess, because Kitchen receptacles should be on 20A circits. A common situation I've seen is for someone to replace a range hood (which is on a 15A general purpose circuit with multiple other loads) with a Microwave unit. It should have been put on a dedicated circuit.

Bill
Posted By: CTwireman Re: 10 amp circuit breakers - 02/21/02 03:21 PM
Bob-
Youre Welcome. [Linked Image] I suggest having an elctrician come take a look at that situation. It is possible that the #10 does not run throughout the entire ciruit, which would make it dangerous to upgrade the breaker to a 20 amp or 30 amp. Someone could have tapped #12 or #14 off of it, seeing that #10 is cumbersome to work with. At any rate, I would suggest professional assistance.
Posted By: mamills Re: 10 amp circuit breakers - 02/21/02 09:56 PM
I'm not certain, but I think the #10 Bob is referring to is the AIC of the breaker, since he says the breaker is a 15 amp. If a single 15 amp breaker is supplying the microwave AND a freezer (and possibly other stuff as well), it's no wonder the breaker keeps tripping. I agree...a new dedicated circuit for the microwave is in order.

Mike (mamills)