Posted By: dugmaze 208V questions - 02/06/02 11:57 PM
My neighbor has three new baseboard heaters and wanted me to install them. They are 208V and I told him that they cannot be used. From my understanding, 208V is 220V three-phase to ground.

Am I correct?

Thanks in advance, Doug.
Posted By: resqcapt19 Re: 208V questions - 02/07/02 12:18 AM
Doug,
Are you sure that they are not dual rated 208/240? Most of them that I have seen are. The wattage is 25% less when on 208.
Don(resqcapt19)
Posted By: Redsy Re: 208V questions - 02/07/02 03:00 AM
The 208 that you refer to is the "high-leg" voltage to ground on a 240/120 volt 3 phase delta connected transformer secondary with on of the windings tapped at midpoint to provide 120 volts. The voltage of one of the phases, usually the "B" phase is about 208 and obviously should be avoided if connecting 120 volt equipment.
There is also a wye connected 208/120 3 phase system where all 3 phases are at 120 volts to ground.
Posted By: dugmaze Re: 208V questions - 02/07/02 03:37 AM
No, I double checked and it is only 208V. So if all I have is 120V single phase or 220V two phase then I can't wire this up.
Posted By: Redsy Re: 208V questions - 02/07/02 12:04 PM
I would not use 208 heaters at 240 volt. But, most of the ones I've seen are dual rated. If they are not dual rated, have him get 240 volt heaters.
BTW, you probably do not have two-phase voltage. It is very uncommon these days. You must mean 240 volt single phase with a neutral. This is the standard residential system.
Posted By: bobc Re: 208V questions - 02/07/02 01:21 PM
Doug,

Three phase 208 is derived from a four wire

wye connected transformer configuration .

120 volts to neutral,208 phase to phase
Posted By: dugmaze Re: 208V questions - 02/07/02 03:00 PM
Somebody must have bought these for a commercial building. Thanks for your help.
Posted By: Steve Miller Re: 208V questions - 02/08/02 12:02 AM
Doing a little basic Ohm's Law here (ignoring the fact that this is AC not DC) you'll find that a 5000 watt (I just used this value for comparison) 208v unit draws 24 amps and has ~8.67 Ohms resistance. The same unit at 240v would draw ~28 amps and put out 6720 watts (R basically stays the same). Their life span will be real short.