Posted By: sid123456 3 phase motor powered by single phase - 02/15/07 12:31 AM
Has anyone ever come across a 3 phase motor powered by single phase? I came across this at a tire shop today. The motor is 3 phase on the name plate but it has a cord with just 3 wires in it. 2 to the motor and 1 grounded to the frame. Open up the pecker head and the taps don't match the high or low voltage diagrams. My boss said I was crazy. That you couldn't do that without a phase converter which there was not. But I've heard an old hillbilly tell me before it was possible.
Posted By: electure Re: 3 phase motor powered by single phase - 02/15/07 01:14 AM
Does it also have a large capacitor (or2) on it?

I've found 3Ø motors on single phase Euro machinery that manufactured their own 3rd Ø.
It is possible, with the use of the appropriate capacitors, etc., to "create" a third phase. It's won't be true three phase, but it will get things spinning the right way.

I'm not about to try to explain the 'how' or the 'why' .... but, since you mentioned that the tap hook-ups were unusual, it is possible that something like that was done.

The other thing you said that caught my attention was "auto shop." I have seen more screwed-up compressor arrangements in auto shops that in all other locations combined. I would almost say "if you saw it in an auto shop, there is no way what you saw was correct."

I suspect that, if you checked, that the motor is performing very poorly. That is, running hot, gobbling power, and not performing anywhere near its' capacity.
Posted By: sid123456 Re: 3 phase motor powered by single phase - 02/15/07 01:31 AM
They do have 2 capacitors..... Very interesting.
Posted By: classicsat Re: 3 phase motor powered by single phase - 02/15/07 02:32 AM
I got free 3Ø 3/4 HP motor one, and run it on 240V with capacitor from an A/C compressor. It is on my power washer.
Posted By: SteveFehr Re: 3 phase motor powered by single phase - 02/15/07 11:44 AM
Good explanation of the circuit on this site: http://www.gwm4-3phase.com/uands/static1.htm

[Linked Image from gwm4-3phase.com]
Posted By: Wolfgang Re: 3 phase motor powered by single phase - 02/15/07 12:40 PM
This way of wiring is quite known in Europe as "Steinmetz wiring". It is limiting the motor to about 70% of its nominal power on 3 phases. So it has to be oversized. In some applications it may overheat due to unregular wave form etc.

On the other hand there is a certain number of applications where smaller 3 phase motors can be wired in Steinmetz alternatively.

Last I saw was a fan in a big blower housing where all necessary data was directly given on the name plate.
Posted By: mikesh Re: 3 phase motor powered by single phase - 02/15/07 04:58 PM
I have seen the big rotophase converters and recently I had a look at a VFD that used a 240 volt single phase input with a variable frequency 3 phase output. It was on a milling machine and the VFD gave him even more speed control than through the gearbox alone.
It was under $1000 CDN for up to 5 horse power.
Posted By: RODALCO Re: 3 phase motor powered by single phase - 02/15/07 06:38 PM
There is an other thread regarding this topic too on ECN with schematics.

It works well. I do the same to convert single phase to three phase in my workshop and then start 3 Ø motors of the running main (3Ø running on 1Ø) motor.

Most motors under 3 HP start directly with no problems from the RST main terminals.
Posted By: iwire Re: 3 phase motor powered by single phase - 02/15/07 08:30 PM
Check out this thread.

I found it interesting.

Hillbilly Sawmill
Posted By: gfretwell Re: 3 phase motor powered by single phase - 02/16/07 02:31 AM
I had a "Gimmee" 3p 3hp gould pump I used on my spa up north for a while but it ran pretty hot and I assumed the power I was wasting could pay for a good high E pump fairly quickly.
I think I had something around 11-12ufd in there. I did try a number of them trying to get as balanced a load on each phase as I could at normal running load. I had a box of 2ufd and 3ufd motor caps I was stringing together, tuning it in. In those days 3p motors were a dime a dozen in the computer fixit biz so lots of guys were trying to find a way to use them. There were several guys with 3/4 hp drill presses, grinders and such since that was a popular motor for disk drives, tape drives and printers.