210.8.... query.... - 11/04/06 12:54 AM
... 210.8 states: A) Dwelling Units
(7) Laundry, Utility, and Wet Bar Sinks. GFCI protection is required for all 15 and 20A, 125V receptacles located within an arc measurement of 6 ft from the dwelling unit laundry, utility, and wet bar sink.
...does that mean the 120 volt washer and dryer circuit has to be on a GFCI as well??
I'd done this in the past and was called back numerous times because the washer motor windings would "simulate" a ground fault on start-up,... so I was told by other sparkies that it's not good to put motor loads on a GFCI because the GFCI "reads" the event as a fault and trips the device... Please advise...thanx...AR
(7) Laundry, Utility, and Wet Bar Sinks. GFCI protection is required for all 15 and 20A, 125V receptacles located within an arc measurement of 6 ft from the dwelling unit laundry, utility, and wet bar sink.
...does that mean the 120 volt washer and dryer circuit has to be on a GFCI as well??
I'd done this in the past and was called back numerous times because the washer motor windings would "simulate" a ground fault on start-up,... so I was told by other sparkies that it's not good to put motor loads on a GFCI because the GFCI "reads" the event as a fault and trips the device... Please advise...thanx...AR