Posted By: bot540 3-phase no nuetral problem - 07/14/06 12:59 AM
I have a customer who wants to add a bunch of kitchen equipment into his resteraunt. The problem is that the 120/208 service with a neutral is maxed out. There is another service, 3-phase (120/208) with out a nuetral that is basically un-tapped. The building used to be a machine shop. Is there a solution to this problem that can be fixed with a transformer?
Posted By: gfretwell Re: 3-phase no nuetral problem - 07/14/06 01:13 AM
208 implies wye so there should be a neutral at the service disconnect panel although it may have never gone beyond there. This is common in computer rooms too. You should be able to exted that neutral to the load if there is room in the pipe.
Posted By: bot540 Re: 3-phase no nuetral problem - 07/14/06 01:32 AM
I checked, but not very hard. The switch gear looks like it is from the '50s. I mean it is really old. It's a metal cabinet and when you open it you see 3 metal bus bars with cartridge fuse holders and lugs for the load side. I'm going to get some pics and post on here.
Posted By: gfretwell Re: 3-phase no nuetral problem - 07/14/06 02:02 AM
Start with the actual service entrance conductors and see if there are 4. It may never get out of the CT can but it really should make it to the MBJ.
Posted By: mahlere Re: 3-phase no nuetral problem - 07/14/06 04:50 AM
otherwise, yes, you can create a neutral with a transformer.
Posted By: gfretwell Re: 3-phase no nuetral problem - 07/14/06 06:00 AM
I can't imagine how you can have a wye without a neutral and 208 always means wye doesn't it? That is how it gets grounded. Is there 208 floating delta somewhere?
Posted By: Texas_Ranger Re: 3-phase no nuetral problem - 07/14/06 09:24 AM
Quote
I can't imagine how you can have a wye without a neutral and 208 always means wye doesn't it? That is how it gets grounded. Is there 208 floating delta somewhere?
No, not really, but wye only means the transformer has a grounded star point, there is no need to provide a neutral conductor anywhere in the system! For example if you only have symmetrical 3ph loads or all loads are connected in delta (don't forget, a wye system allows you to connect loads both in wye or delta) you won't need a neutral conductor. That's why European motors only have a 3w+ground cord supplying the three phases. Old 3ph plugs didn't even have a neutral terminal. So maybe you need to go all the way up to the transformer.
Posted By: Alan Nadon Re: 3-phase no nuetral problem - 07/14/06 01:01 PM
250.24 (B) requires the grounded conductor, if there is one, to be brought to the service .
Some installations using 3 phase only try, and sometimes do, omit it but it is needed as a fault path to the transformer.
Check the weather head and see if the drop from the utility co is 4 wire or 3 with a messenger. The messsenger will be bonded at the point of origin.
Alan--
Posted By: Texas_Ranger Re: 3-phase no nuetral problem - 07/15/06 01:59 PM
*smack* I forgot the NEC doesn't allow systems that are grounded via local ground rod only. That rules out a wye system w/o neutral.
Posted By: gfretwell Re: 3-phase no nuetral problem - 07/15/06 03:58 PM
As I said upthread, computer rooms did not bring the neutral beyond the service disconnect since the standard was only line to line loads. It should still be in the service disconnect enclosure where it gets attached to the main bonding jumper and the grounding electrode. I suppose if you held your nose real tight that connection could be in the metering equipment but I can't see it being very much farther toward the line side.
Posted By: Scott35 Re: 3-phase no nuetral problem - 07/16/06 05:03 AM
bot540, I have a few questions for you, regarding this Project:

Quote

The problem is that the 120/208 service with a neutral is maxed out. There is another service, 3-phase (120/208) with out a nuetral that is basically un-tapped.

1: Are there 2 individual Services - meaning there are 2 separate gear sections, each one has a kWh meter and a Service Disconect, or is there only one gear section with a kWh meter + Service Disconnect?

2: How close is the gear section without the common grounded neutral conductor, from the gear section with 4 wires?

3: If bringing a grounded conductor into the 3 wire gear section is close to impossible, would an option to drive 3 Phase 3 Wire, or Single Phase 2 Wire (208VAC) equipment from the 3 Wire gear section be feasable?

4: When you say "The Service With The Neutral Is Maxed Out"; does this mean:

***A: The Service's Capacity is inadequate for the connected loads (as viewed by load calcs against the gear's rating &/or the Main Breaker of the system),

or...

***B: The Transformer feeding this Service Section has a lower kVA rating, than what will be required for the new connected loads,

or...

***C: There are no more spaces available for Circuit Breakers.

5: Can you see the Transformer which is feeding the Tenant Suite on your project?

If Transformers mounted on poles, are all 3 the same size - with only one wire coming from the "right side" secondary bushings on each Transformer, and a "common" wire, connected to each of the "left side" secondary bushings on each Transformer, which also comes off the Transformer on the left side, and is run with the 3 other wires?
This indicates a 4 wire Wye connection.

If you only see 2 Transformers, and they are connected together "in parallel", you have an open delta.

If there are 3 Transformers, with the "Middle" Transformer being twice as large as the outer 2 - and they are all connected 'in parallel", this is a closed delta.

In either delta case, if the "larger" Transformer has 3 wires connected to the secondary bushings, the system is a 4 wire delta (or a 3 wire with center tap ground).
If one Transformer has only 2 wires made up to the bushings, this is likely to be a 3 wire Delta.

6: If you are able to find the Transformer which feeds the Tenant Space, can you follow the Service Feeders to the point of attachment on the premisis?

*If Overhead: Does the drop from the Transformers / Pole attach to a riser, and from there get tapped into 2 separate risers?
Also, how many conductors?

* If Underground: Lift up one of the access covers on the Pad (in front of the Transformer), and see how many Service Feeder ducts run to your project (do not enter the Vault!!!).

Your scenario sounds like a very commonly done "Dual Service" option, found in buildings circa 1950's thru 1970's - having a Service Capacity not exceeding 400 amps per "Section".

These have two individual Service Sections - each with a kWh meter and Service Disconnect.

One Section is named "Lighting", and is the Service Section with the Grounded Conductor used + bonded to equipment and G.E.S.

The other Section is named "Power", and uses only the 3 Ungrounded Conductors.
It's enclosure + equipment is bonded to the "Lighting" Section via Equipment Bonding Jumper only - no system conductor is Grounded nor bonded at this service section.

The typical way of feeding the separate sections, is to use separate feeders + ducts for each service section, and the "separated feeders" get tied together either at the pole, in the Vault of a Pad Mounted Transformer, or just outside of the Weatherheads of 2 separate overhead service risers.

Granted, these were normally 120/240V 1 Phase 3 Wire "Lighting" Sections, and 240V 3 phase 3 Wire "Power" Sections, but I have also seen a few with 208Y/120V 3 Phase 4 Wire "Lighting" Sections, and 208V 3 Phase 3 Wire "Power" Sections.

Anyhow, let me know what you find out.

p.s. post those images!!!

Scott35
Posted By: LarryC Re: 3-phase no nuetral problem - 07/16/06 05:36 PM
Quote
if you held your nose real tight that connection could be in the metering equipment

Is the neutral required for metering?

Or is it that the neutral, the main bonding jumper and the ground rod connection are sometimes made in the metering equipment?

LarryC
Posted By: gfretwell Re: 3-phase no nuetral problem - 07/17/06 03:31 AM
The ground electrode sometimes ends up in the metering equipment around here and they might have terminated the neutral there.
Posted By: Trumpy Re: 3-phase no nuetral problem - 07/17/06 06:45 AM
It makes me wonder, with a Wye service, why the Neutral doesn't come into a busbar in the main panel.
Sure from there, you can set up a load in Star or Delta.
Having a Neutral bus would help in the panel.
Just my thoughts.
[Linked Image]
Posted By: bot540 Re: 3-phase no nuetral problem - 07/18/06 01:49 AM