Posted By: derater water in conduit - 06/28/06 02:11 AM
Ah hem, gulp; well someone didn't tape over his 3" 90 UG service pvc and I'd bet I'll find it full of water tomorrow. Looking for tips on getting it out. I may have to fire myself . Thanks
Posted By: frenchelectrican Re: water in conduit - 06/28/06 02:22 AM
There is few tricks you can try get most of the water out of the conduct

1} use shop vaccum to suck much water as possible

2} use the compressed air to blow the water out [ make sure no one is standing on the oppstite end other wise will get soaked from " fontaion " or shower ]

but dont expect to get all of the water out of the conduct 100 percent of it espcally if run in UG set up


Merci , Marc
Posted By: NORCAL Re: water in conduit - 06/28/06 04:06 AM
Use shop vac and a conduit mouse, should do a reasonable job.
Posted By: Celtic Re: water in conduit - 06/28/06 09:08 PM
...it's that the reason we use conductors with a "W" pre/suf fix in the them [Linked Image]