Why is 120/208 volt 3 phase used mostly in commercial buildings, and not 120/240v like residential single phase homes? (My question is not about the single or 3 phase, but about 208 vs 240v).
Depends on the Customer + the time period when the Building was developed.
If the "area" where the commercial client leases the Building happens to have customers on the distribution system who use more large Motor loads than "Lighting" loads, these Buildings most likely would have been fed from a 4 Wire Delta.
Same client's Building - if larger than 20,000 square feet for example, may have been fed from either a 480Y/277 Volt 4 Wire Wye, or a 480 Volt 3 Wire Ungrounded delta - or even a 240 Volt Corner Grounded 3 Wire Delta.
Other areas and design bases of Buildings - large and small, may be fed from 208Y/120 Volt 4 Wire Wye setups.
All depends on the customer types, the buildings' designs, the existing / available PoCo systems, and most importantly, the time period of development + area.
Currently in my area (Southern California) for a "No Large Motor Use Commercial Project", the only way to get a completely new 240 Volt Delta System - either 3 or 4 wire, open or closed, is to have a very special reason for it + pay $$$ for it,
or maybe threaten the Design Engineers with Guns or such (just joking!)
Even when the connected equipment becomes majority 3 phase Induction Motors, it's under special permission.
Same goes for anything of the 480 and 600 Volt 3 Phase Deltas - Grounded and Ungrounded.
The usage of 4 wire Wye services for Commercial / light Industrial customers is more useful than Deltas.
These systems are well suited for the "common" commercial enviroment where a majority of equipment will be Line to Neutral load connections, and less than 40% of connected loads will be heavy L-L-L or L-L loads.
If there is a need for a full 240 Volt rated system, then it's the client's obligation to install an SDS.
Along with this, there is an issue of people getting screwed by the "Stinger Leg" of a 4 wire delta, along with misapplications of connected equipment to 4 Wire Open Deltas - causing the PoCo's Transformers to release smoke.
I personnaly do not mis PoCo supplied Delta Systems - had dealt with many in the past, but mostly because of the crazy things that occur when people that have little or no knowledge of them, start messing with them; or connect equipment to them.
The disadvantage of 4 wire Wye connected secondaries is Zero-Sequenced Harmonics reflected into these windings are not canceled out - as they would be in a Delta connected Secondary - but this "problem" can be overcome with proper design and selection of connected equipment, and increased Apparent Power sizing for Transformers (or using "K Rated" Transformers).
The problems of applying "too low of voltage" to equipment is quickly going away.
Back in the 1970's, I remember all too well of the "it needs to be 240 volts, not 208 volts" conflicts.
This was applied to Heating type equipment, as well as Motor Loads, Welding Loads and Battery Charging Loads - all of which had no previsions to set jumpers on a "208 Volt" tap, or even a "200 Volt" tap - only had "220 Volts", "240 Volts", "460 Volts", "480 Volts", "575 Volts" and "600 Volts".
Eventually, Manufacturers started to give "a 200/208 Volt Option" for equipment, and doing so made them more appealing to customers, as they did not have to install any "special SDS Transformer" to run that equipment, and they could run it directly from their existing electrical system.
What is the 3 phase 208v wild leg usually used for in commercial panels?
This is simply a "result" of having a 4 Wire Delta system, using Transformers with 240 Volt Secondary Windings connected in a "Parallel Delta" configuration, and having one Transformer's Secondary Winding "Center Tapped" to obtain the Neutral Conductor for a 120/240 System.
The "Stinger Leg" or "High Leg/Phase" is not an item of design - and is not intended to be used for Line to Neutral load connections!
It becomes present in Panelboards (as the Conductor color coded "Orange") when the Panelboard is a 3 Phase type, where there will be a combination of 3 Phase 3 Wire Branch Circuits and 1 Phase 3 Wire Multiwire Branch Circuits used.
A very common design technique for Buildings with 4 Wire Deltas, was to use 1 Phase 3 Wire Panelboards - fed with Lines "A", "C" and the Center Tapped Neutral, where only 1 Phase loads were used (like in Office spaces and such), and using 3 Phase Panelboards - fed with Lines "A, B & C" only - no Grounded Conductor (Neutral), where only L-L and 3 Phase loads were used (like in the warehouse shop area or for HVAC equipment).
Also since romex (NM) is not allowed in commercial buildings, has anyone ever seen an application where 277/480v was used, using NM? NM insulation is good for 600v.
I have only seen a few small commercial locations, where a previous EC had used NM Cable.
It looks very odd, but it is not illegal - per the NEC.
If the Design Specifications for a certain project does not allow NM Cable, but the NEC (or ammended version of model code) will allow NM Cable for that given Commercial Project, the Design Specifications of the Contract Documents wins!