Posted By: Dnkldorf 240/120 D - 04/05/06 01:54 AM
Can you run a 208 single phase motor of this 240/120D 3 phase service?


Dnk...

[This message has been edited by Dnkldorf (edited 04-04-2006).]
Posted By: gfretwell Re: 240/120 D - 04/05/06 02:11 AM
I have always heard you shouldn't run L/N loads on a wild leg unless it was a real 3 transformer delta. It is supposed to screw up the voltage across the open side compared to the closed side.
Posted By: Bob Re: 240/120 D - 04/05/06 03:31 AM
You need to look at the motor name plate. If
the motor is rate 208/240 its ok. If not you may need to install a bucking transformer.